Dedicated power


I'm looking to run a dedicated 30a and dedicated 20a line to my system directly from the fuse box. 
I currently have some florescent lights and some other junk on the line so I'm hoping it will be an improvement. Things sounds like they are straining somewhat when you crank things up. The amp will go on the 30a line and the digital stuff on the 20a. 
Anyone done this and saw improvements? 
mofojo
Hmm maybe I will stock with single line. I guess other issue with 2 is it's a real bear to run these. I am in basement and where the fuse box is there is no basement under it (concrete). We figured out a way to run it but it is tight and the 2 lines would need to be close together for most of the run, maybe inducing noise?
 I'll ask my electrician what the local code is about the outlet. If I can use a 20a outlet on a 30a line I will do that. If not I will stick with 20a.
How long are your runs?  Unless they are more than 30' you are just as well running 12 gauge Romex.

If much longer, then run a 60A to a subpanel, and then run short 20A circuits to each outlet.  The advantages of a 60, in addition to lower voltage drop, is that the code may let you get away with not running conduit for it. Check your local ordinances.

Never put more than a 20A breaker on a normal 15/20A outlet, regardless of wiring. It has no audible benefit, and serious safety issues.
https://www.youtube.com/watch?v=fe2nt5BMKsE

Hello, does anyone recognize the silver record weight, Its definitely not he stock weight 
that comes with this Pro-ject Xtension Evo 10 ?
thx
PRO-JECT XTENSION 10 Evolution Gramofon turntable Plattenspieler - gramofony Pro-ject Project AUDIO VIDEO SHOW PRAHA 2019

I’d go twin 20amp heavy gauge shielded lines and use Synergistic Research Orange outlets or hospital grade outlets on up. Lots of beefy ones out there. If you do nothing else getting rid of stock wall outlets should help.

I could not run new lines but once everything from the wall out was ungraded even my wife (who couldn’t care a fig) said she thought the sound was better.

If you go with a power conditioner get a top one.

Thinking of the entire electrical supply and all wires as a components makes doing improvements easy.