@ orthomead
+1 almarg post on 12-15-2019
almarg9,244 posts
12-15-2019
8:14pm
Regarding keeping the two AC legs from becoming significantly unbalanced, I would infer from the literature on your VAC amps that they operate primarily in class AB, since only the input and driver stages are described as operating in class A. And given their 200 watt rating in mono mode I suspect that aside from occasional very brief dynamic peaks in the music each amp will probably be supplying well under 100 watts to the speakers, with the two amps together consequently drawing no more than about 500 watts of AC. With the system as a whole probably drawing no more than 800 watts or so most of the time, including the sub amp. Which seems to me to be sufficiently low that keeping the legs in balance is a non-issue, regardless of which of the three approaches is chosen.
Using Al’s (almarg) calculations for total average energy usage of 800 watts would not be a problem, imo, putting the four 20 amp dedicated branch circuits on the same Line , leg.
One 120V 20 amp (2400 watts) branch circuit would easily handle a 800 watt load. Spreading, separating, the loads of your audio equipment across 4 branch circuits will not change the total connected load.
800 watts / 120 volts = 6.7 amps. 6.7 amps will not cause a significant imbalance load on the electrical service of your home.
The average portable vacuum cleaner has an FLA of 12 amps. A portable electric space heater 1500 watt @ 125V, 12 amps. An average microwave oven 1200 watts, 10 amps @ 120V.
Using 10-2 with ground Romex (NM sheathed cable) where the total length is 45ft should rule out the chance of ground loop hum..... Should..... I can’t count all the threads I have read over the years where monoblocks were/are used where the user is fighting ground loop hum problems.
Here is just one running now.
https://forum.audiogon.com/discussions/krell-kas-amplifier-hum @Atmasphere explains most ground loop hum is caused by the audio equipment itself. Poor design in the way the designer connected the circuit ground/signal ground to the AC mains safety equipment grounded chassis of the equipment.
Jim