a Krell 250wpc stereo amp survived in spite of not being connected to any passive line cond oddly enough.
They have those big transformers protecting everything after that, kind of how series mode protection works, unless they have enough capacitance coupling the inner to outer coils.
So the component’s fuse itself is enough general protection from electrical surges.
Um, aberyclark no. Fuses disconnect on high current, low speed events. A surge from lightning is high voltage, high speed, and relatively very low current, until it finds a path through silicone. Once the fuse trips, it means the surge has already shorted something. Also, see differences between fast and slow blowing fuses.
Surge protectors activate on high speed, high voltage events. A fuse could take 0.1 second to activate. A lightning surge can occur in microseconds.
Which is why series mode surge suppression is the way to go. Zero activation time to the leading surge edge, and non-sacrificial components.
McIntosh uses Series Mode Protection in their top of the line $10,500 conditioner, but Furman has it in their $180 strips.
Also, cross contamination is real. Use an Elite or use multiple Furman strips to keep your digital/streaming devices from contaminating your clean zone.