Jea48,
Check this from the 2011 NEC. 250.130(c)1
250.130 (C)
(C) Non grounding Receptacle Replacement or Branch
Circuit Extensions. The equipment grounding conductor
of a grounding-type receptacle or a branch-circuit extension
shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) For grounded systems, the grounded service conductor
within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar
within the service equipment enclosure
The cold water pipe is part of the Grounding Electrode System. The key word is System, which includes the cold water pipe. Check 250.50 for description of GES.
This is discussed in length on Mike Holts web site.
As far as the correct size of the equipment grounding conductor for 15amp circuits #14awg copper or 20amp circuits #12awg as per 250.122 2011 NEC but nothing wrong with #10 also.
Did not mean to slam GS5556 but a blanket statement like that can get people hurt. Peace T. J.
Check this from the 2011 NEC. 250.130(c)1
250.130 (C)
(C) Non grounding Receptacle Replacement or Branch
Circuit Extensions. The equipment grounding conductor
of a grounding-type receptacle or a branch-circuit extension
shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) For grounded systems, the grounded service conductor
within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar
within the service equipment enclosure
The cold water pipe is part of the Grounding Electrode System. The key word is System, which includes the cold water pipe. Check 250.50 for description of GES.
This is discussed in length on Mike Holts web site.
As far as the correct size of the equipment grounding conductor for 15amp circuits #14awg copper or 20amp circuits #12awg as per 250.122 2011 NEC but nothing wrong with #10 also.
Did not mean to slam GS5556 but a blanket statement like that can get people hurt. Peace T. J.