To follow up....If your using metal conduit and boxes for your new circuits make sure that your electrician DOES NOT bond your new outlets to the boxes via any jumper wire.Doing so will defeat the isolated ground on your hospital grade plugs.The goal is to keep your audio circuits ground path separate from your house wiring.The reason being is if your house uses metal boxes with bonded outlets ,as many modern homes do,your metal conduit via it's connection to your bonded panel enclosure becomes part of that ground path allowing stray voltages to make there way into your audio circuits.One advantage of the metal conduit in this set up is that it acts like a shield in many of the better power cords where the shield wire is connected at the load end ( or your panel in this case) only.Same principle at work here......
- ...