No one at a hospital checks the force required to remove a plug.
(My boss is going to laugh when he hears that.)
08-09-06: joemh22@yahoo.com
joemh22@yahoo.com,
Really.....
So did your boss laugh?
Quote Chapter 4 of NFPA 99 (2005 edition) addresses the electrical systems in health care facilities. It requires the electrical installation to be in accordance with NFPA 70, National Electrical Code (4.3.2.1). Following are some of the commonly referenced requirements: Leviton Hospital grade plug and receptacle testing. Hubbell white paper for testing of hospital grade receptacles used in Canada. Cheap basic Receptacle tension tester. |
I just wanted to add, in addition to the robustness of the connection and overall build quality, hospital grade receptacles are built to be wired with a redundant ground conductor (required by NEC Article 517, Health Care Facilities). It will NOT do this on it's own however. You need to wire back to the panel with hospital grade AC (aka hospital grade BX) or hospital grade MC (not as common). With the AC/BX cable you have the metal armor w/ drain wire as your first ground path (which is how regular AC/BX works) and an additional insulated conductor for a second redundant ground (unique to hospital grade BX). With hospital grade MC (uncommon), you have two insulated grounding conductors (instead of one, which regular MC has). Note the metal armor on MC cable is not listed as a ground. |