Since there are electricians seeing this thread would like to ask them if 12/2 Romax is OK for 20 amp circuits. Is there some reason why 10/2 seems to be preferred in many audiophile installations? Is it the concept of "Overwire and Underbreaker?"
Per NEC (National Electrical Code) #12 copper wire is the bare minimum wire size for a 20 amp branch circuit. NEC does not prohibit using a wire size larger than #12. Usually a larger wire size is used for VD (Voltage Drop) that may occur on the conductors of the branch circuit due to the connected load. The connected load does not need to be a continuous connected load. It could be caused by a fluctuating load.
The size of the breaker, overcurrent device, dictates the ampere rating of the branch circuit. The OP has a 30 amp breaker, therefore the circuit is 30 amps. Per NEC you can not install a 20 amp rated receptacle on a 30 amp branch circuit. Per code the breaker must be 20 amp.
Here is an old Link, but still holds true for when a breaker is supposed to trip if overloaded.