Yes, I have a dedicated 240 volt line, made from 10 AWG Romex and a 30 amp breaker.
01-01-15: Jafreeman
The 30 amp breaker does nothing more for the available power the ISO xfmr can draw from the main electrical panel than the correct size 20 amp breaker would. The total power that the ISO xfmr can deliver to the connected load is limited by the circuit breaker mounted in the front of the ISO xfmr unit. That breaker is there to protect the unit from a continuous overload or short circuit.
The current carrying contacts inside a 30 amp breaker are exactly the same size as a 20 amp breaker. The only difference is the thermal and magnetic trip unit settings.
The #10 wire was a good idea but it should be connected to a 2 pole 20 amp breaker.
There is a reason why the manufacture of the ISO xfmr specs a 20 amp circuit, there in a 20 amp breaker. He is following NEC Code which says a 20 amp rated receptacle can only be connected to a 20 amp breaker.
No need to lift the ground--the house ground is not involved,
I hope that does not mean a separate earth ground, ground rod, that is not connected to the main grounding system of the electrical service of your home.
There is a reason why NEC Code requires the neutral conductor of a separately derived power system, (there in the neutral conductor of the secondary winding of an ISO xfmr), to be connected to the main grounding electrode system of the main electrical service. It can be connected to it at any point. (Technically a safety equipment grounding conductor is not part of the grounding electrode system, though it connects to it.)
If you do have a dedicated earth ground that is totally separate from the main grounding system of your home I hope you did not break the equipment grounding conductor/connection that connects to the ISO xfmr unit from the 240V branch circuit that feeds the unit. That could be dangerous.
The Earth does not possess some magical mystical power that sucks nasties from an audio system.
.