What you're describing to me sounds like you've taken two male plugs and connected a 16 gauge wire between the ground tabs with no other wiring between the hot & neutral tabs. You intend to plug this into the Hydra and into your wall outlet, hoping that it will act as a common ground for the entire system.
If that summary is correct, i would suggest doing the following. Unplug your Hydra from the wall and unplug your components from it. Take a multimeter and measure the resistance between the ground tab of the AC plug you'll be using and each individual ground tab on the other outlets. So long as they all measure very low in resistance, this should work fine. Personally, i would have used a heavier gauge wire as that ground will act as a default for all of the components simultaneously, not just one. Given that your ground wire to the outlet is probably 12 gauge at best ( unless you've rewired ), that is what i would use here.
While you've got the Hydra disconnected, measure the resistance from the ground tab to the chassis of the component. This should be as low as from ground to ground on the AC sockets of the Hydra. Then measure the resistance from the chassis to the neutral tab on a couple of the outlets on the Hydra. This should read very high if not infinity. The lower that it reads, the less efficient it will be at shielding the internal connections from incoming RFI. At the same time, the ability to reduce EMI from being radiated out of the chassis will have also been reduced. It would be relatively simple to correct this if you run into this situation, but it would require modifying / rewiring the internals of the Hydra.
Hope this helps to answer your question and gives you the info that you were looking for. Sean
>
If that summary is correct, i would suggest doing the following. Unplug your Hydra from the wall and unplug your components from it. Take a multimeter and measure the resistance between the ground tab of the AC plug you'll be using and each individual ground tab on the other outlets. So long as they all measure very low in resistance, this should work fine. Personally, i would have used a heavier gauge wire as that ground will act as a default for all of the components simultaneously, not just one. Given that your ground wire to the outlet is probably 12 gauge at best ( unless you've rewired ), that is what i would use here.
While you've got the Hydra disconnected, measure the resistance from the ground tab to the chassis of the component. This should be as low as from ground to ground on the AC sockets of the Hydra. Then measure the resistance from the chassis to the neutral tab on a couple of the outlets on the Hydra. This should read very high if not infinity. The lower that it reads, the less efficient it will be at shielding the internal connections from incoming RFI. At the same time, the ability to reduce EMI from being radiated out of the chassis will have also been reduced. It would be relatively simple to correct this if you run into this situation, but it would require modifying / rewiring the internals of the Hydra.
Hope this helps to answer your question and gives you the info that you were looking for. Sean
>