Almarg, I've always wondered about the code to use only one ground rod as well. I have never heard an explanation.
02-14-12: Sarcher30
Sarcher30,
There is no limit of the maximum number of grounding electrodes (ground rods), only the minimum required.
What NEC does require is that they must all be tied electrically together. When all tied together they are considered by NEC as one grounding electrode.
Several 8ft ground rods is not necessary better than one 30ft deep driven ground rod. What matters is the rod/earth resistivity...... The lower the earth soil resistance the better. 3 ohms or less is considered very good.
I would bet very few houses even come close. NEC code says if the earth resistance is greater than 25 ohms the ground rod shall be augmented by one additional ground rod. The earth resistance could be 60 ohms but all NEC calls for is one additional rod. The earth resistance still could end up higher than 25 ohms...... NEC code is satisfied with the one addition rod.....
At least in my area, I have never heard of a residential electrical contractor ever checking the earth ground resistance. I have only seen it checked on industrial facilities. Special equipment is required for the test.
http://www.cpccorp.com/deep.htm
http://www.erico.com/public/library/fep/strike/LT0540.pdf
.