I presume it is a stock plug,regular style,but Krell said you can plug it in a 30amp service..This is where i am confused and is why I was looking for fellow 600/700 cx owners with a dedicated 30amp receptacle
30 amp receptacle for Krell 700cx
I will soon recieve a 700cx and was told to use a 30 amp circuit for this amp.I also concur as I may run 2.7ohm speakers later.I would like to know what receptacle is best for this amp.I have no problems with power out of my panel and 10gauge wiring(I currently have 4 20amp circuits).
thanks john
thanks john
- ...
- 8 posts total
Mclsound, The Full Power Balanced 700cx,http://www.krellonline.com/assets/support/0162_020_MAN.pdf I assume the unit uses a NEMA 5-20P plug. Thus you will need a NEMA 5-20R receptacle. A NEMA 5-20R 20 amp receptacle can only be installed on a 20 amp branch circuit per UL, NEC, and most importantly the manufacture of the receptacle. Krell should of incorporated soft start circuitry in the amp but instead, and I am only guessing here, is telling their dealers to tell their customers to use a 30 amp breaker if nuisance tripping occurs. Bad call.... Subject: Breaker nuisance tripping>http://www.lyntec.com/body_faq-msp.htm Subject: Breaker nuisance tripping Do all 20 amp circuit breakers respond to inrush surges the same way? Instead of using a 30 amp breaker I suggest you ask the electrician who will be installing the dedicated circuit for the Krell to see if the electrical panel manufacture makes a HM 20 amp breaker for the panel. I would still have #10 awg solid core wire installed for the branch circuit wiring. Example of an HM 20 amp breaker. http://ecatalog.squared.com/fulldetail.cfm?partnumber=QO120HM Something else I would suggest if you will not be leaving the amp on 24/7 and will be turning on and off the amp daily you may want to use a heavy duty UL listed 20 amp receptacle. Hubbell manufactures a highly respected heavy duty recept. The Porter Port is a Hubbell heavy duty recept. I believe Wattgate also uses a Hubbell. Maybe others.... |
How does Krell define a 30-amp circuit? By the circuit breaker or the wire size? If you install a 30-amp breaker, an inspector will look for 30-amp wire (#10 or fatter) and for 30-amp rated receptacles. Those receptacles will not fit the standard 15-amp power cord plug with parallel blades pointing up and down. Installing a 30-amp breaker on a circuit with standard receptacles is a code violation. If you install the standard receptacles - parallel blades up and down - you can only install a maximum of a 20-amp breaker. That's because the power cord plug will limit the circuit to 15-amps. A 20-amp circuit has a 20 amp breaker that feeds two to ten 15-amp receptacle/plugs for a total steady load of 16-amps. Or a single 20-amp receptacle (blades are perpendicular) feeding a 16-amp appliance. A 30-amp circuit feeds either a dedicated 30-amp receptacle or multiple 30-A receptacles with no more that 24-amp appliance power draw total. So when you get your amp, look at the plug. If it is a standard plug, you can use 30-amp wire in the wall (the Krell power cord is probably 10/3, which is 30-amp rated) but you can only use a 15-amp receptacle (or a combo 15/20-amp). But you cannot use a 30-amp breaker in most places. Check with your local BD. Now you may ask why do amps with 15-amp plugs say in their specs that they draw a maximum power of, say, 6000 Watts -- which is 50-amps single phase. Won't that melt the 15-A plug and/or receptacle? No, because that is not a steady power draw. The over current is not greater than one half the power cycle and the 20-amp breaker lets that 50-amps pass since that breaker will have a 10,000 amp withstand rating for that time period. The danger is a fault within the equipment that draws a steady, say, 24 amps. A 30-A CB will happily let that pass but a 20-A CB will thermal trip and protect your property. |
Correct Link for error link in my last post. http://www.lyntec.com/body_faq-msp.htm For example of a 20 amp standard breaker verses a HM breaker, lag time / inrush current. |
- 8 posts total