Photon46, I advise against opposed blade dampers located near the outlets. If you are going to install them, put them well upstream of the outlets, because the sound they regenerate has a chance to be reduced before it arrives at the outlet. I agree with Jeffreybehr's suggestion of larger flex ducts, but just make sure they are substantially larger than the existing metal ones, because the pressure drop in flex duct is an order of magnitude greater than in sheet metal duct, which your fan system probably won't be capable of handling which means not enough air will be supplied into the room. If you can only make the duct slightly larger than what exists, consider ducts made of fiberglass duct board which although they won't provide as much sound attenuation as flex ducts, the pressure loss isn't too much more than sheet metal. Slowing the air down is strongly advised, and oversize the outlets a bit. Using an opposed blade damper in the duct well upstream of the outlet instead of closing the damper on the register supplying into the room can help, too.
Dealing with HVAC vent air flow noise?
We've just replaced our split HVAC system with upgraded capacity and higher quality/efficiency components. One aspect of the upgrade is a 1/2 ton higher capacity air handler with a multiple speed blower. While the system is much quieter overall than the previous one, during the heat of the day when the air flow is ramped up to it's greatest arflow, I notice more air noise than before coming from the vents. It seems that if a larger outlet or an additional outlet were installed, resulting lower air volume/friction/turbulence would reduce noise in the listening area. Have any of you dealt with a similar problem? What worked for you?
- ...