Hevac1,
Similar to mine, except I have a 5KVA 480/240-240/120. Wired 240V to 480V input and X1, X4 is +/- 60V with X2/X3 connected ("optionally" to neutral).
Just tested with analog clamp-on and I got 3.5A (average)per 240V leg and 7.5A on the outlets (93%). Unloaded, it was 1.5A on the 240V side, which was higher than I expected. Analog meter is not precise.
Wiring 120V to the 240V inputs proved inconsistent. We are going beyond the design and rating but it seems to help to stay as close as possible. I'm also using a GFCI on the balanced outlet, for safety.