Kingrex said:
I replace MC because of ground issues. I experience it in the field. I really could care less about EMF issues. You can deal with that in the field. More EMF issues arise behind your rack than in the wall. If you know how to run wire. EMF is teally one of your lesser issues.
You are the first person that has raised ground issues with MC cable, at least on the audio forums I follow.
Could you expand on the problems you have experienced? If it is ground loops, it’s not the MC cable itself causing the ground problems. From what I have read is the audiophile that had MC cable installed are happy with the MC dedicated branch circuit(s).
.
I really could care less about EMF issues..
Where did that come from??? Not from my above post. 🤔
The subject matter of my post is about induced voltage by the magnetic fields generated by the Hot and Neutral current carrying conductors onto the EGC of the branch circuit wiring.
Therein, NM cable vs MC cable. If you read the two Links I provided it is proven, by measurements, MC cable does a better job of preventing the magnetic fields generated by the current carrying Hot and Neutral conductors from inducing a voltage onto the EGC.
FYI, The bigger the connected load on the branch circuit conductors the bigger, the greater strength, of the magnetic fields. So it would stand to reason a big hungry power amp connected to one dedicated circuit would draw more current than say a CDP on another dedicated circuit.
The EGC of the branch circuit with the power amp would be more susceptible to the chance of an induced voltage onto the EGC of an NM cable branch circuit that an MC cable branch circuit. (Especially long branch circuit runs). Therein with MC cable there would be less of chance of a difference of potential between the two EGCs of the two branch circuits than NM cable. YMMV...
The worst branch circuit wiring method would be to loosely pull conductors in a conduit. Worst yet is more than one dedicated circuit with conductors loosely pulled in the same conduit. Sure fired way to create ground loop hum problems.
.