@lowrider57
Square D QO. Good Choice.
No doubt he carries a Square D QO 120 breaker in his service van. Still wouldn’t hurt to tell him the breaker is a QO 120 breaker. Only a Square D QO breaker will work in the panel.
No need to have the audio equipment hooked up to the Equi Core unit. If he needs a load you can always use pretty much anything with a cord and plug you have in your home for a load.
You might prepare a place on the dining room table for him to look at the Equi Core unit So he doesn’t have to get down on his hands and knees. Make sure he has good lighting. Natural lighting works best.
Also you might mention the transformer has a 60/120V split phase secondary winding. The two outer 120V leads are both ungrounded that connect to the duplex receptacle AC Line, Mains, contacts.
The secondary winding center tap neutral lead is bonded, grounded, to the chassis and to the equipment ground contacts on the duplex receptacle outlets.
(NEC ARTICLE 647 Sensitive Electronic Equipment.)
Jim
Square D QO. Good Choice.
No doubt he carries a Square D QO 120 breaker in his service van. Still wouldn’t hurt to tell him the breaker is a QO 120 breaker. Only a Square D QO breaker will work in the panel.
No need to have the audio equipment hooked up to the Equi Core unit. If he needs a load you can always use pretty much anything with a cord and plug you have in your home for a load.
You might prepare a place on the dining room table for him to look at the Equi Core unit So he doesn’t have to get down on his hands and knees. Make sure he has good lighting. Natural lighting works best.
Also you might mention the transformer has a 60/120V split phase secondary winding. The two outer 120V leads are both ungrounded that connect to the duplex receptacle AC Line, Mains, contacts.
The secondary winding center tap neutral lead is bonded, grounded, to the chassis and to the equipment ground contacts on the duplex receptacle outlets.
(NEC ARTICLE 647 Sensitive Electronic Equipment.)
Jim