@lowrider57
For some reason the above post, I originally posted last night, was corrupted after it looked fine after I posted it. The post this morning is the same without the corrupted part as seen at the top sentence of the post last night. I then deleted the post.
With that out of the way.....
I would like you to preform a test when you get a chance. Plug a vacuum cleaner into the wall outlet of the 20 amp dedicated circuit that has been tripping the breaker. Most walk behind vacuum cleaners have a so called 12 amp motor. That means if the motor is loaded, vacuuming carpet, it will draw 12 amps, or slightly less... That is a good load test for the branch circuit wiring as well as the branch circuit breaker.
It should power up fine without tripping the breaker. But,.... there is all them breaker trips and resets.... One thing for sure if the vacuum runs just fine that clears any finger pointing at the branch circuit wiring and breaker causing the problem.
You still need to hire an electrician and have him trouble shoot your situation. At the very least have the 20 amp breaker in the sub panel replaced.
I kept forgetting to ask, what manufacturer made the sub panel and breaker?
Example, Square D? Square D QO? Square D Homeline?
The electrician will be more than qualified to look at the Equi=Core unit. You can save some money by having the top cover already removed before he looks at it. You might ask him, when you call him, if he has a Megger? If he does ask him to bring it with him.
Megger is a trade name of an insulation tester. Example of:
https://www.grainger.com/product/MEGGER-Insulation-Tester-54JH70?ef_id=EAIaIQobChMI_Pu6tfHx5wIVx0XVC...
I would also let him know what manufacture made the sub panel. On the inside of the hinged cover it should list the manufacturer as well as the model number.
That way he will know for sure he has the 20 amp breaker in his Service Van when he comes to your home. Time is money....
Jim
.
For some reason the above post, I originally posted last night, was corrupted after it looked fine after I posted it. The post this morning is the same without the corrupted part as seen at the top sentence of the post last night. I then deleted the post.
With that out of the way.....
I would like you to preform a test when you get a chance. Plug a vacuum cleaner into the wall outlet of the 20 amp dedicated circuit that has been tripping the breaker. Most walk behind vacuum cleaners have a so called 12 amp motor. That means if the motor is loaded, vacuuming carpet, it will draw 12 amps, or slightly less... That is a good load test for the branch circuit wiring as well as the branch circuit breaker.
It should power up fine without tripping the breaker. But,.... there is all them breaker trips and resets.... One thing for sure if the vacuum runs just fine that clears any finger pointing at the branch circuit wiring and breaker causing the problem.
You still need to hire an electrician and have him trouble shoot your situation. At the very least have the 20 amp breaker in the sub panel replaced.
I kept forgetting to ask, what manufacturer made the sub panel and breaker?
Example, Square D? Square D QO? Square D Homeline?
The electrician will be more than qualified to look at the Equi=Core unit. You can save some money by having the top cover already removed before he looks at it. You might ask him, when you call him, if he has a Megger? If he does ask him to bring it with him.
Megger is a trade name of an insulation tester. Example of:
https://www.grainger.com/product/MEGGER-Insulation-Tester-54JH70?ef_id=EAIaIQobChMI_Pu6tfHx5wIVx0XVC...
I would also let him know what manufacture made the sub panel. On the inside of the hinged cover it should list the manufacturer as well as the model number.
That way he will know for sure he has the 20 amp breaker in his Service Van when he comes to your home. Time is money....
Jim
.