Good one, Bob. Yes, almost all 15 and 20a male ACs and many duplexes have the same contacts, just different geometry. IEC320 connectors continue to be the weak link here. (The affordable Schurter 4781.0100 IS a good one for high current, but only after you modify its contacts.
For true 20a use I suggest hard-wiring around the IEC even if it's the horizontal-spade true 20a. Too bad this isn't often an option. I found it of further interest that during a conversation with one of the IEC320 manufacturers about the 10-12AWG size limit of their terminal beds that he noted that most of the PC manufacturers who buy from him simply shave their 8-10AWG conductors down to fit them into the IECs! Sigh.... Be careful what you pay for, guys, and Happy Holidays.
For true 20a use I suggest hard-wiring around the IEC even if it's the horizontal-spade true 20a. Too bad this isn't often an option. I found it of further interest that during a conversation with one of the IEC320 manufacturers about the 10-12AWG size limit of their terminal beds that he noted that most of the PC manufacturers who buy from him simply shave their 8-10AWG conductors down to fit them into the IECs! Sigh.... Be careful what you pay for, guys, and Happy Holidays.