As for the 20 receptacle it did not cause your problem.
If you have a volt meter I suggest you check the voltage and polarity at the recept.
Small straight slot contact is the Hot.
"T" shaped slot is the neutral.
"U" shape hole contact the safety equipment ground.
*Hot to neutral you should read 120V nominal.
*Hot to safety equipment ground 120V nominal. (This will tell you the polarity is correct.) Reversed polarity would not have caused your problem.....
*Neutral to safety equipment ground zero.
Could be the cheap intergraded amp shot crap all on its own.....
As for NEC code though.... a 20 amp receptacle can only be installed on a 20 amp branch circuit. Two or more 15 amp rated receptacles can be installed on a 20 amp branch circuit.