I’m 10’ from a dedicated panel wires in wall ending at two hospital grade outlets.
What you have is basically 10ft extensions of equipment power cords. 10ft of branch circuit wiring does little, if anything, to decouple the power supplies of digital equipment from analog equipment.
With connecting tabs broken I used 4 x 12 gauge Romex starting with 4 x 20 amp breakers.
I assume you hired an electrician for the electrical wiring installation. Per NEC code when the two receptacles of the duplex receptacle are split and are fed from separate circuit breakers, both outlets shall be de-energized by a single handle action for electrical safety. Single action, use of a 2 pole circuit breaker or two single pole breakers using an approved, Listed, breaker tie.
Problem? Just a guess the sub panel is wired as a 120/240V electrical panel. Not a 120V only sub panel.
Best practices accepted by many audiophiles, is all 120V audio equipment that will be connected together by wire interconnects, should be fed by circuit breakers that are connected to the same bus, Leg, Line, in the 120/240V electrical panel. All to Line 1 or all to Line 2. Not from both L1 & L2 though.
Another problem I see is the close proximity of different dedicated circuits to one another. Therein induced voltage, noise, from the Hot and neutral current carrying conductor of one circuit to the other. Again it defeats the purpose of more than one dedicated circuit to feed audio equipment.
I posted this above in this thread, not sure it you read them.
Some reading material for you:
An Overview of Audio System Grounding & Interfacing
Read page 16, and pages 31 thru 36.
.
Integrating Electronic Equipment and Power
Read pages 11, 12, &13.
.