What wire to use instead of Romex


I want to install a dedicated 20amp outlet (likely an AQ NRG). The run from the main panel in the garage to my living room above is relatively short - maybe 25 or 30 feet. Because of HOA rules/regs, I cannot use Romex. Wires in the garage must be inside conduit. I will run 10AWG, but I'm unsure what other specs I should implement. Should I use solid core or stranded? Should it be copper? Is BX the way to go? I've read where using stranded silver or silver tungsten is best, but I'd be concerned about the silver oxidizing/tarnishing over time, especially at the junction points where the wire has no insulation. Is it important to twist the three (including ground) wires or will they perform just as well if run side-by-side? 

roccity

Dedicated lines are a great upgrade. Based on all of your questions and rules I think it might be a good idea to get some help from an electrician. Don’t overthink this, plain copper will do the job.

@roccity Wrote:

Is BX the way to go?

NO! Do not use BX for audio see below:

For dedicated audio lines I would go with Type MC Galvanized Steel Metal Clad Cable 10 AWG. It has better EMI and EF shielding versus aluminum armor. FWIW, I have four dedicated lines for audio, one for each monoblock amp, one for analog and one for digital. 😎

Mike

 

Thanks @zlone and @ditusa 

I'm definitely going to have an electrician do the install for me.  I'm okay with working on 110, but I don't trust myself around the main panel!  Looking at MC cables on Amazon and HomeDepot.com, they all seem to be aluminum-clad, not steel, and both stranded and solid core copper are available.

New Q1: Stranded vs Solid Core?
New Q2: Any tips on where I can find steel-clad? 

Thanks again!
Patrick

 Solid Core copper conductors with insulated ground, not stranded. The electrician will know where to get steel-clad MC cable.

Mike

No help here, sorry. I was under the impression that solid core is code, though I am sure someone else can comment. I just ran Romex for my dual lines, but it is only about 15 feet.

Depends on the local code requirements that your HOA is following. In some states, though not common, hollow (metal/Alum) conduit is required to be bent and set, then solid wire fished through. MC flex cables may only be used for certain lengths of runs. It all depends... If you don't know your local code requirements, as said before, consult your electrician first before picking products. A licensed electrician will know the code.

Use an electrician for installation. But specify the wire. They will think you are crazy, every time I have done it they have. They will refuse to believe that different wire sounds different. I just asked them to humor me. Definitely 10 gauge. I think there is specialty wire. I'm sure someone here will specify it.  I used 10 gauge Rolex. Excellent improvement in my system. 

Because of HOA rules/regs, I cannot use Romex. Wires in the garage must be inside conduit.

That also may be the AHJ (Authority having Jurisdiction) electrical code in your area as well. In Chicago IL only EMT conduit is allowed in residential housing. MC or AC/BX, nor flexible metal conduit is allowed. Going from memory in NY City, NY Romex is not allowed.

You need to contact the Electrical Contractor you will be using. He will know what you can use. Also have a copy of the HOA requirement for him to read.

As for using EMT conduit I would suggest you ask the Electrician to twist the Hot and Neutral conductors together before pulling them in the conduit. Pull the EGC, (Equipment Grounding Conductor) along side the twisted pair when installing the branch circuit wiring in the EMT conduit. The EGC could be #12awg green insulated solid copper wire if you use #10awg copper wire.(FWIW, the electrician may tell you you don’t need an EGC insulated conductor in the conduit. Per NEC the EMT conduit is an approved EGC. It’s your call... I would have him install the EGC insulated conductor anyway.  

 

Solid core wire only for the Hot and neutral conductors. Tell the electrician you want solid wire not stranded. He is going to resist the suggestion. Hold firm.

.

The run from the main panel in the garage to my living room above is relatively short - maybe 25 or 30 feet.

Did you guesstimate Up, over, across, and down?  

.

Some reading material for you:

An Overview of Audio System Grounding & Interfacing

 Read page 16, and pages 31 thru 36.

.

Integrating Electronic Equipment and Power

Read pages 11, 12, &13. 

.

@jea48 @ghdprentice @nwres @zlone @ditusa 

The distance measurement is a down-over-across-farther down rough measurement.

Flexible conduit is allowed by code. My town's fussy code inspector saw what I was using for me EV charger outlet run and was fine with it. Romex is perfectly acceptable too as far as code is concerned, but not a good idea to put inside conduit. As I said before, the HOA wants any wires in the garage inside conduit, presumably for a uniform appearance as the garage is a shared area with four bays, one for each condo in the building (there are 86 buildings).

I fully expect to get a funny look from any electrician when I specify, "Metal Clad (galvanized steel, not aluminium) 10 AWG Solid Core Copper w/Insulated Stranded Ground. Twist the hot and neutral together before pulling the wires and run the ground along side."  I'll just shrug my shoulders and smile when he shakes his head and/or rolls his eyes.

Thank you all for the input. It's very appreciated!

That will be an interesting discussion. 😀 Good luck, and let us know how it sounds when you are done. 
 

10 AWG Solid Core Copper w/Insulated Stranded Ground.

MC cable is not made that way. All solid conductors or all stranded conductors. 

.

Twist the hot and neutral together before pulling the wires and run the ground along side.

Nothing in the NEC code says he can’t twist the Hot and neutral single conductors together before pulling them in the conduit. If the electrician says NEC does not allow it get him to tell you the Article and section... Now the AHJ, has the final say though.

.

Romex is perfectly acceptable too as far as code is concerned, but not a good idea to put inside conduit.

NEC code doesn’t prohibit pulling NM sheathed cable, (Romex trade name) in EMT conduit.

For #10-2  Romex in the garage area the electrician would use 3/4" EMT conduit.  

EMT conduit

Example, #10awg THHN/THWN solid copper wire   

  

I’ll just shrug my shoulders and smile when he shakes his head and/or rolls his eyes.

Who is paying who for doing the Job? 

What he should be thinking. If you got the money, I got the time...

What are you going to say if he tells you #12awg wire is used for a 20 amp circuit? Not #10 wire. Solid #10 ??? Stranded is all you need. 

.

Did you take the time to look these over?

Some reading material for you:

An Overview of Audio System Grounding & Interfacing

 Read page 16, and pages 31 thru 36.

 Just go to page 31, 32, 33, & page 35. Note, page 35 in the chart shown, the hot and neutral conductors twisted together tested the best, followed by MC cable.  

.

Integrating Electronic Equipment and Power

Why use MC cable over Romex? 

Why twisted twisted pair is better than MC.

Read pages 11, 12, &13. 

.

FWIW, NEC code is bare minimum electrical safety standards. NEC could care less how your audio system sounds. 

Is the electrical wiring installation electrically safe? Code is satisfied.

 

.

@jea48 (and @ghdprentice @nwres @zlone @ditusa)  I did read from the two sources you linked. To be honest, a lot of it went over my head. Taking everything into consideration, would it be more advisable to:

A. Use the pre-made steel-clad with all three solid-core wires twisted
B. Use two solid-core wires twisted together with one stranded along side for ground and pull the three wires through flexible steel conduit

Oh, and should I specify THHN wire?

I also should mention that my HOA doesn't want Romex inside conduit in the garages, so that is not an option for me, While I THINK it's okay by code, I have been told that Romex can generate heat inside conduit.

A. Use the pre-made steel-clad with all three solid-core wires twisted

 If the HOA will allow it in the garage. Continuous unbroken run from the Electrical panel to the wall outlet.

Problem? I’m not sure where the Electrician will buy the steel armored MC cable. Maybe at an electrical wholesale house??? He may have to buy a 250ft roll, $$$

My guess is the electrician will say he can only get the aluminum armored MC cable.   

 Example  

.

Southwire, 10-2 MC aluminum armored cable Website.

Quote:

 " THHN/THWN conductors rated 90°C dry available in sizes 14 AWG through 2 AWG, and a green insulated grounding conductor. The conductors are cabled together and a binder tape bearing the print legend is wrapped around the assembly. Aluminum interlocking armor is applied over the assembly."

End of quote.

.

Go to page 12

Metal Clad (MC) is manufactured in both steel and aluminum with twisted conductors that help reduce AC magnetic fields. Although the steel jacket helps reduce AC magnetic fields, the twisting of conductors has the greatest effect on reducing these fields.

Another benefit is the constant symmetry of the phase conductors with respect to the grounding conductor which greatly reduces voltage induction on the grounding wire.

.

 

Make sure he doesn’t buy AC/BX cable! You don’t want that stuff to feed you audio equipment!

FYI, though Anti Short bushings are not required by NEC code for MC cable, I highly recommend you tell the electrician you want them installed anyway. If he says you don’t need them. Tell him, you want them anyway. They are cheap and it will take the electrician about 15 seconds to install one. 

Example:

Pretty simple to install.

 

"Because of HOA rules/regs, I cannot use Romex" It's this kind of ignorance that ensures I'll never live where there is an HOA. What business it is of theirs what kind of wiring you or anyone else uses if used correctly? 

@jea48

Next week I'm going to stop by a local electrical supply house that I've been to before and buy the cable myself. I should probably get a more accurate measurement in case I can purchase by the foot and save a few bucks versus buying a 50-foot run (if it's even available in that length).

I didn't even know about anti-short bushings. Thanks so much for the links. At first I thought it was more like a grommet to line the hole into the panel box. Seeing the video of how they're installed, it definitely makes sense to me to use them. I'll grab a couple either at Home Depot or the supply house, so long as they don't obscenely overcharge for them and if they're not already included with the cable.  I'll keep you and the others here in the loop. Have a great weekend!

Hello- 10 gauge wire matches with a 30 amp breaker in the electrical panel. The possible problem with #10 wire and a 20 amp breaker is that if the copper wire heats up excessively, the breaker will not trip in order to save it, and the insulation around the copper will melt, causing a fire inside the wall. This has been the cause of many house fires. For audio components, this should not be an issue, as they are not heating devices (like space heaters, etc.). 

the HOA wants any wires in the garage inside conduit, presumably for a uniform appearance as the garage is a shared area with four bays

Leave it to the Karens in the HOA to dictate the appearance of the INTERIOR of a garage.

10 gauge wire matches with a 30 amp breaker in the electrical panel ...

Not necessarily. Using 10AWG wire with a 20A breaker can help reduce voltage drop.

The possible problem with #10 wire and a 20 amp breaker is that if the copper wire heats up excessively, the breaker will not trip in order to save it ...

The wire should never heat up, the breaker should trip at 20A. No problem.

@roccity said:

Next week I’m going to stop by a local electrical supply house that I’ve been to before and buy the cable myself.

You might want to check with the HOA first. Exposed MC cable will not be as pleasing to the eye as EMT conduit. MC exposed kind of looks like installing Romex exposed on a wall. You can support the heck out of it and it still doesn’t look pretty...

Questions:

How much of the the exposed MC cable will be seen in the garage before it enters the wall of dwelling unit?

What is the garage wall finish of the wall it will be installed on? Example, wood studs covered by drywall? Cement block? Other?

Horizontal elevation off the floor of the MC cable? Distance down from the ceiling?

Is the electrical panel surfaced mounted to the wall? 

Vertical length of the MC cable above the electrical panel  before it is installed horizontally?

Can you post a picture of the electrical panel and the area the MC cable will be installed?

.

I’m 10’ from a dedicated panel wires in wall ending at two hospital grade outlets. With connecting tabs broken I used 4 x 12 gauge Romex starting with 4 x 20 amp breakers. Clean, Independent, bendable, code, happy. 
Cheers 
 

I’m 10’ from a dedicated panel wires in wall ending at two hospital grade outlets.

What you have is basically 10ft extensions of equipment power cords. 10ft of branch circuit wiring does little, if anything, to decouple the power supplies of digital equipment from analog equipment. 

 

With connecting tabs broken I used 4 x 12 gauge Romex starting with 4 x 20 amp breakers.

I assume you hired an electrician for the electrical wiring installation. Per NEC code when the two receptacles of the duplex receptacle are split and are fed from separate circuit breakers, both outlets shall be de-energized by a single handle action for electrical safety. Single action, use of a 2 pole circuit breaker or two single pole breakers using an approved, Listed, breaker tie.

Problem? Just a guess the sub panel is wired as a 120/240V electrical panel. Not a 120V only sub panel.

Best practices accepted by many audiophiles, is all 120V audio equipment that will be connected together by wire interconnects,  should be fed by circuit breakers that are connected to the same bus, Leg, Line, in the 120/240V electrical panel. All to Line 1 or all to Line 2. Not from both L1 & L2 though.

Another problem I see is the close proximity of different dedicated circuits to one another. Therein induced voltage, noise, from the Hot and neutral current carrying conductor of one circuit to the other. Again it defeats the purpose of more than one dedicated circuit to feed audio equipment.

I posted this above in this thread, not sure it you read them.

Some reading material for you:

An Overview of Audio System Grounding & Interfacing

 Read page 16, and pages 31 thru 36.

.

Integrating Electronic Equipment and Power

Read pages 11, 12, &13. 

.

@jea48 

Questions:

How much of the the exposed MC cable will be seen in the garage before it enters the wall of dwelling unit?

The living room wall where the outlet will be is directly above the garage door. The cable will run from the ceiling of the garage down a foot or so, then to the left over the pedestrian door, along the wall with the panels, and down to the lower of my two panels (wired together to function as a single panel rather than a main and a sub). Or, it could run across the ceiling, then down to my panel. That'd be a shorter run.

What is the garage wall finish of the wall it will be installed on? Example, wood studs covered by drywall? Cement block? Other?

Wood studs with sheetrock/drywall, with plywood over it where the panels are.

Horizontal elevation off the floor of the MC cable? Distance down from the ceiling?

Is the electrical panel surfaced mounted to the wall? 

Vertical length of the MC cable above the electrical panel  before it is installed horizontally?

I haven't taken measurements, but you can probably ballpark them from the photos. And yes, surface mounted panel(s).

GaragePanels

@roccity 

That angled flexible metal conduit feeding the small load centers is butt ugly... frown

The HOA shouldn’t question your use of MC cable. Good thing about 10-2 solid copper wire MC cable, the solid #10awg copper wire stiffens the metal armor so it can look more presentable to the eye. 

 

@roccity 

It just occurred to me, your Condo electrical wiring is not fed from any of the load center panels in the photo you posted. Where is the electrical panel that feeds your Condo unit located? I assume somewhere in the Condo.

Why are you wanting to fed a dedicated circuit from one of the load centers in the garage? I’m not sure what the feeder ampacity rating is for the load center panel you are planning to use, or the existing loads on the panel.

More info is needed.

Like where is the panel that feeds your Condo unit in regards to where the new dedicated audio circuit wall outlet will be? 

@jea48 

My condo has a subpanel in the kitchen with individual breakers for the different circuits in my home. The two panels in the garage (the Square-D panels with one sitting above the other) are my main panel. If you look closely, you'll see a 100-amp tandem breaker in the top panel labeled "Condo." This feeds the subpanel in my kitchen.  The electric meters are on the exterior of the wall to which the panels are mounted.

My thinking is that the total load on my main panel remains the same as I won't be adding any usage but rather just redistributing it, and so exceeding any capacity limit is not an issue.

Let me know if this makes sense and clears things up for you.

Can't it be run inside the wall? Any competent electrician should be able to.

@rwwear 

Can't it be run inside the wall? Any competent electrician should be able to

I suppose it could, but if I understand what you're asking, that would entail having to cut into the drywall every 16 inches and drill holes through the studs. Running it across the ceiling or walls is simpler and cheaper, if not more aesthetically pleasing.   

@roccity said

My condo has a subpanel in the kitchen with individual breakers for the different circuits in my home. The two panels in the garage (the Square-D panels with one sitting above the other) are my main panel.

OK.

.

If you look closely, you’ll see a 100-amp tandem breaker in the top panel labeled "Condo." This feeds the subpanel in my kitchen.

Edit:  " tandem " to 2 pole breaker ( 2 pole 100A,  240V breaker) .

I can’t make out what’s written on the labels. It looks like there are a few 2 pole 240V breakers in the two panels. Air conditioning?  Water Heater? Electric car charger? Other?.

So, The angled GF, flexible metal conduit, out the top of the panel is a 100A feeder that feeds the sub panel in the kitchen. 

.

The electric meters are on the exterior of the wall to which the panels are mounted.

OK.

Just curious, is there a 2 pole 100A, 240V main breaker outdoors fed from the load side of the electric meter socket? Just curious...

Yes, I too would feed the new dedicated 120V 20A branch circuit from the main panel in the garage. (But I will ask is the sub panel in the kitchen closer to where you want to install the branch circuit wall outlet? How much closer?)

Will the HOA require you, actually the electrical contractor/electrician, to pull a electrical permit? If yes I wonder if the electrician will be required to install a 20A AFCI breaker in the electrical panel. Hard to tell from the photo but it looks to me like the two panels are Square D QO. I believe a 1 pole 20A AFCI breaker will work, fit, if required

FWIW, From what I have read your area in NY State is still working under the 2020 NEC code.  

.

Downside? Lightning protection. Are lightning storms common in the City you live in? Because of the distance from the branch wall outlet, there in the length of the branch circuit wiring from the main electrical service equipment may be less than 30ft, a plug-in Type 3 point of use SPD (Surge Protection Device) is not recommended (allowed), by NEC, UL, NEMA, therefore the Manufacturer of the Type 3 SPD. 

IF your area is subject to frequent lightning storms I would suggest you have the electrician install a Type 2 SPD at the main panel in the garage. Top of the line residential  Siemens or Eaton Type 2 SPDs get very good customer reviews.

.

I really would like to know if there is a 2 pole main disconnect breaker outdoors on the load side of the electric meter socket for your electrical service. If yes that is where the electrical service is connected to Mother Earth.

.

As for this:

@rwwear said:

Can’t it be run inside the wall? Any competent electrician should be able to

@roccity  response:

I suppose it could, but if I understand what you’re asking, that would entail having to cut into the drywall every 16 inches and drill holes through the studs. Running it across the ceiling or walls is simpler and cheaper, if not more aesthetically pleasing.

@roccity 

Hopefully the electrician you hire will be experienced in what he does. Layout, layout, layout... Hopefully he practices the 6 Ps. Prior Planning Prevents Piss Poor Production. His attitude should be he can do anything... If you have the money, he has the time.

Question, is there a Condo above yours? Or maybe an attic space? 

FWIW, I don’t think you are going to like the looks of MC cable surfaced mounted on your wall(s) and ceiling. IF you are married you best run the idea past your wife first...

.

@jea48 

Edit:  " tandem " to 2 pole breaker ( 2 pole 100A,  240V breaker) .

I stand corrected. My electrical knowledge is limited (but I give myself credit for at least not referring to the outlet as "The Holes" like the one shady "electrician" George Costanza hired cheeky).

I can’t make out what’s written on the labels. It looks like there are a few 2 pole 240V breakers in the two panels. Air conditioning?  Water Heater? Electric car charger? Other?

There’s a main breaker for the power coming into the panel, one for power going to the main unit, one for a 120v outlet in the garage, one for A/C and one for the 240v EV charger (NEMA 4-50) outlet.

So, The angled GF, flexible metal conduit, out the top of the panel is a 100A feeder that feeds the sub panel in the kitchen. 

That is correct.

Just curious, is there a 2 pole 100A, 240V main breaker outdoors fed from the load side of the electric meter socket?

I believe that’s the one that I have labeled "Main" on the left side of the top panel. Outdoors, there’s just the meter.

But I will ask is the sub panel in the kitchen closer to where you want to install the branch circuit wall outlet? How much closer?

It’s definitely a much shorter run from the proposed outlet to the garage.

Will the HOA require you, actually the electrical contractor/electrician, to pull a electrical permit? If yes I wonder if the electrician will be required to install a 20A AFCI breaker in the electrical panel. Hard to tell from the photo but it looks to me like the two panels are Square D QO. I believe a 1 pole 20A AFCI breaker will work, fit, if required.

A permit is not needed. I actually spoke with the board president about my plans, and he gave me a verbal go-ahead to do the work without a variance from the HOA.  An AFCI breaker would only be needed if the outlet were to be installed in the garage.  When I had the outlet installed for my EV charger, I was told by code enforcement that if I had hardwired the charger, a standard breaker would have been acceptable.  The idea being that other devices could potentially be plugged into the outlet and then said devices might be left outdoors and exposed to the elements, creating a risk and necessitating the additional protection.

Are lightning storms common in the City you live in?

We get a few good storms a year. All electrical in my neighborhood is underground. I’m guessing that reduces the risk, though I’m sure it doesn’t entirely eliminate it.

IF your area is subject to frequent lightning storms I would suggest you have the electrician install a Type 2 SPD at the main panel in the garage. Top of the line residential  Siemens or Eaton Type 2 SPDs get very good customer reviews.

I just looked up Type 2 SPD’s on Amazon. They’re not tiny.  I don’t know if there’d be space in the panel for that as well as the breaker. I admit that I don’t even know how it would connect. I should probably open the panel and take a photo.

@jea48 

Thank you for your interest, I’m using 4 Single pole breakers with nicely separated independent 12 gauge wires, there is no need or code to use breaker ties, I want them independent. I’ve a 100 amp panel servicing little else, the audio ends at 2 hospital grade outlet boxes (tabs broken code legal). Suggesting this akin to 10  foot Power cables is well… Ridiculous. And finally Decouple Digital from analogue Through your AC wiring and fuse panel ? Are you suggesting home buyers Should revamp the supplied electrical circuit so as to use their audio systems ? That’s a hard cell and certainly on the placebo side of things in my opinion. Thankfully I have clean power there is zero noise. What I do and have done is certified electrician and code approved. My son is a fibre optic engineer, I’m licensed, audiophile fussy and have help. I do believe in diminishing returns and hate snake oil of any kind. I did this to have three of my high-powered boat anchor amps separated should a problem arise. Smaller equipment is independent. 

Cheers 

@roccity 

I should probably open the panel and take a photo.

If you feel safe doing so... Get a good well lit close up piture of the interior of the main panel.

What is the size, handle amp rating, of the breaker that feeds the kitchen sub panel? (Number is on the front of the breaker switch handle.)

An AFCI breaker would only be needed if the outlet were to be installed in the garage.      

That would be a GFCI breaker is required for a garage receptacle outlet. An AFCI (Arc Fault Circuit Interrupter) breaker is not required in a garage. 

The residential  Siemens or Eaton Type 2 SPDs mount to the exterior of the panel enclosure. Not inside of the enclosure of the panel. There appears to be room for an SPD on the top, left  side, of the panel enclosure. 

DO NOT buy either the residential  Siemens or Eaton Type 2 SPDs from Amazon. Amazon.com IS NOT an authorized dealer. Manufacturer’s warranty would be void...

.

How about this:

Question, is there a Condo above yours? Or maybe an attic space? 

FWIW, I don’t think you are going to like the looks of MC cable surfaced mounted on your wall(s) and ceiling. IF you are married you best run the idea past your wife first...

And to add, I assume your Condo is on an opposite wall of the garage? Approximately the same ground level? Correct?  (The common wall will be fire rated. Any idea the wall material, thickness of wall?)

How about a length of the branch circuit wiring from the garage panel to the wall outlet?

If 30ft or less you might want to consider using #12awg solid copper single conductors. Twist the Hot and neutral together as I mention in another post. Use EMT conduit in the garage to a pull box, (No joints/splices) then transition to 700 Wiremold in the condo unit. 700 WM is surfaced mounted. Colors come in white and Ivory.

700 Wiremold Conductor fill chart  Easy fit for a twisted pair of #12 solid conductors plus a #12 solid EGC green insulated ground wire.

(You could use 500 WM instead. Width is the same as 700 WM. Height is less.  Electrician still should not have any problem installing the twisted pair and the straight run #12 EGC along side the twisted pair of #12s in the 500 WM raceway.)

Wiremold 700 Series Small Raceway, Ivory    

Legrand/Wiremold® 500 & 700 Series  

Example Youtube video how to install WM 

Installing WM is not for a novice. If the electrician does not have many, many hours of experience installing WM don’t you be his first job. What you see, is what you get!

Note, for your installation, project, I would not run WM up the middle of a wall or across the middle of ceiling. I would install the WM over to an inside corner of a wall and go up or down the wall. You might end up using a few more WM 90s, but you will end with a better looking job, imo... 

Sometimes WM looks less noticeable if ran around a room just above wall wood base. With care it can be installed through a wall to the next room on the other side of a wall. (Fairly easy if wall are drywall. NOT so easy if wood lath and plaster.) Requires drilling a hole through drywall, wall stud, and drywall on the other side of the wall. IMO, not for a novice... Some drywall spackel using a small mud knife is required to patch around the WM after the WM is installed. Paint patch as needed.

When you get to the location of where the wall outlet will be located, use a flat 700 WM 90 degree fitting to go up the wall to the WM outlet box mounting plate. Leave the box off until wire is installed in 700 WM raceway.

Forget about trying to install #10 solid in 700 Wiremold. The electrician would destroy the insulation covering trying to install it in the Wiremold. #12awg solid will be hard enough... Usually stranded wire is used in 500 WM or 700 WM raceway.

Use the hidden WM support clip to support the 700 WM raceway. Not the ugly saddle support strap.

The electrician will twist the Hot and neutral conductors together and install the ground wire along the side.

Cost wise? more expensive than the MC cable. More pleasing to the eye though. Trust me MC will look ugly inside your Condo ran exposed. Even painted, it will look ugly.

Just curious. How high, tall, is the wood base along your walls. Is it painted or stained. How about a good photo of the wood base.

 .

@1971gto455ho said:

@jea48

Thank you for your interest, I’m using 4 Single pole breakers with nicely separated independent 12 gauge wires, there is no need or code to use breaker ties, I want them independent. I’ve a 100 amp panel servicing little else, the audio ends at 2 hospital grade outlet boxes (tabs broken code legal).

In response to my post on  

Per NEC code when the two receptacles of the duplex receptacle are split and are fed from separate circuit breakers, both outlets shall be de-energized by a single handle action for electrical safety. Single action, use of a 2 pole circuit breaker or two single pole breakers using an approved, Listed, breaker tie.

2020 NEC

Quote:

210.7 Multiple Branch Circuits. "Where two or more branch circuits supply devices or equipment on the same yoke or mounting strap, a means to simultaneously disconnect the ungrounded supply conductors shall be provided at the point at which the branch circuits originate."

end of quote.

Like I said in my post, it’s an electrical safety thing. 

.

Best regards,

Jim

.

What is the size, handle amp rating, of the breaker that feeds the kitchen sub panel?

100amp

That would be a GFCI breaker is required for a garage receptacle outlet. An AFCI (Arc Fault Circuit Interrupter) breaker is not required in a garage. 

Just did a little Google research and learned what an AFCI is. I'm not sure if code requires it, but if it does, I'm sure the electrician will let me know.

DO NOT buy either the residential  Siemens or Eaton Type 2 SPDs from Amazon. Amazon.com IS NOT an authorized dealer. Manufacturer’s warranty would be void.

Thanks for the tip!

Question, is there a Condo above yours? Or maybe an attic space? 

No. The buildings here are all two stories: 1 ranch unit, 2 townhouse units (living/dining/kitchen downstairs, bath and bedrooms upstairs), and 1 terrace unit (small terrace off of dining room above the front door) with the entire living area (except the front door, a small entryway and a coat closet) above the four garage bays.  Above the terrace and townhouse units is a common attic. The ranch has its own attic.

FWIW, I don’t think you are going to like the looks of MC cable surfaced mounted on your wall(s) and ceiling. IF you are married you best run the idea past your wife first.

I'm not very worried. As you saw, the garage is not particularly great looking as it is, and it'd be worse - all sheetrock with tape and spackle - if I hadn't thrown up a coat of white paint to brighten it up.

If 30ft or less you might want to consider using #12awg solid copper single conductors. Twist the Hot and neutral together as I mention in another post. Use EMT conduit in the garage to a pull box, (No joints/splices) then transition to 700 Wiremold in the condo unit. 700 WM is surfaced mounted.

I like the idea of going over spec and using 10AWG. Seems like Wiremold would make the outlet install much easier, but is there a variety that can fit the larger gauge? As far as aesthetics, I could live with a short run (about 12") coming straight up from the floor to the bottom of a surface-mounted outlet box. There'd be no need to run any Wiremold along walls or baseboards. Even if more expensive, using EMT would allow me to follow your recommendation of twisting the hot with the neutral but not the ground. And yes, I certainly want a single run of each wire with no splices.

Installing WM is not for a novice. If the electrician does not have many, many hours of experience installing WM don’t you be his first job. What you see, is what you get!

I will definitely ask how experienced he is with it before going that route!

Trust me MC will look ugly inside your Condo ran exposed. Even painted, it will look ugly

What I had originally envisioned is an outlet inside the wall like any other, with the wiring going down through the wall and into the garage.

Hopefully the Street View image of a building in my complex and my remarkable artist's rendition help you better understand the layout of everything. And once again, thanks for all of your input. It's very valuable and very appreciated.

Panel (Open)BuildingBuilding2

@roccity 

Nice photo of the bottom surfaced mounted electrical panel. How about a photo of the interior of top Main Electrical service panel. That’s the one I wanted to see.

Breakers in the Square D panel in the above photo are their Homline style. OK. I like the Square D QO better. The QO has plated copper Bus. Homeline has aluminum bus  

@roccity said:

As far as aesthetics, I could live with a short run (about 12") coming straight up from the floor to the bottom of a surface-mounted outlet box.

Is that the extent of the new branch circuit wiring there will be in the Condo? About 12"? I'm confused... Is the new wall outlet in the Condo, on the same common wall with the garage? 

"coming straight up from the floor to the bottom of a"

Is the wall in the condo wood studs with drywall? 

.

Both panels were put in to replace the original panel which did not have enough room for another breaker for my NEMA 14-50 outlet for my EV charger. A single larger panel would not fit in between the panel of one of my neighbor’s to the right and the house panel (power for common elements) to the left. I had to go to Home Depot earlier today. While I was there, I did in fact pick up a Homeline breaker to have on hand (20 AMP, single pole).

Is the wall in the condo wood studs with drywall?

Yes - wood studs with drywall. Constructed circa 1973/1974.

Is the new wall outlet in the Condo, on the same common wall with the garage? 

Yes. It's a short, straight run from the outlet down to the garage - just as it appears in the illustration I created above.

Top Panel (Open)

@jea48 

Best Practices:

It's recommended to use separate, appropriately sized 20 amp circuits with their own breakers and wiring to feed each half of the duplex receptacle. This ensures proper protection and avoids potential hazards.

Proper Method:

1. Separate Circuits:

Each 20 amp circuit should be run from its own 20 amp breaker in the electrical panel to its respective half of the duplex receptacle.

2. Appropriate Wiring:

Use 12 gauge Romex for both circuits, as it is rated for 20 amps.

3. Proper Termination:

Ensure the hot (black), neutral (white), and ground (bare or green) wires are correctly connected to their respective terminals on each half of the duplex receptacle. 
This is code ! 
 

Cheers 

@1971gto455ho 

It's recommended to use separate, appropriately sized 20 amp circuits with their own breakers and wiring to feed each half of the duplex receptacle.

I never thought about doing two runs to one duplex outlet. That's really kickin' it up a notch! I'm going to consider doing that. FYIW: My plan was to plug my stereo power amp directly into one outlet (manufacturer recommends NOT using any type of power conditioner) and my power conditioner into the other, which will have my preamp, DAC and streamer plugged into it.

@roccity  

Using appropriate wiring and breakers on a split duplex has been around for years and it is most definitely code and designed to be used that way as well. It is essentially no different than using a single outlet on a duplex box. Wiring must be done properly and you have absolutely no issues with safety. 
I did this because each one of my amps requires its own 20 amp breaker and I wanted to minimize dry wall and stud issues. The changes are well indicated in the panel and in the duplex box so any future people opening either will realize that multiple breakers have to be turned off. 
 Chreers

@1971gto455ho Said:

Best Practices:

It’s recommended to use separate, appropriately sized 20 amp circuits with their own breakers and wiring to feed each half of the duplex receptacle. This ensures proper protection and avoids potential hazards.

Proper Method:

1. Separate Circuits:

Each 20 amp circuit should be run from its own 20 amp breaker in the electrical panel to its respective half of the duplex receptacle.

2. Appropriate Wiring:

Use 12 gauge Romex for both circuits, as it is rated for 20 amps.

3. Proper Termination:

Ensure the hot (black), neutral (white), and ground (bare or green) wires are correctly connected to their respective terminals on each half of the duplex receptacle. 
This is code ! 

This is code ! 

No it is not. I posted word for word from the 2020 NEC code book.

I will look tomorrow for when NEC 210.7 Multiple Branch Circuits, the code edition year it was added to the NEC code book.  You may have wired your outlets the way you have them before 210.7 Multiple Branch Circuits was added to the NEC. 

Best practices is no guarantee that it follows or meets NEC or AHJ code. 

Your quoted material might be old. It should be updated to meet current NEC code. Or at least for the NEC code edition your state is still using. 

Please post the Website for the quoted material in your post. 

.

@jea48  

Do let me know for curiosity sake, it’s CSA approved here. I also run into many houses where 12 three was used in duplex boxes, that can get complicated and I personally don’t recommend it anymore, but it is legal. And I should add and don’t know that this would make a difference but the four wires and two duplex are in a double box. 
 

 

@1971gto455ho 

2011 NEC 210.7 was added to NEC.

FWIW, in the US if you wired the duplex outlets as you have them wired before the 2011 NEC was adopted by the state, or AHJ governing body for the county or city you live in, they would be grandfathered in.

I have no Idea what Canada electrical code says.

FWIW, I usually look up the username of a member before responding to a post of theirs. Don’t know why I missed looking you up. My bad. I wasted your time as well as mine on the subject.

I found this doing a quick Google search.

CEC Versus NEC: What’s the Difference?

.

@roccity said:

Yes. It’s a short, straight run from the outlet down to the garage - just as it appears in the illustration I created above.

Best and cheapest way is to have the electrician install 10-2 solid copper MC cable.

You will save on labor and material. Labor is your biggest cost.

He may even be able to run the MC cable up inside the wall and recess the electrical outlet box. Just a suggestion for the electrician use a deep i gang cut-in switch box. He will appreciated the added space for make up of the duplex outlet to the #10 solid wire.

FYI if you would like 4 receptacle outlets have him install a 2 gang deep cut-in switch box for two duplex outlets.