Bundus is right on about wire choice.I've done exactly as he describes with excellent results.The electrician should know that a separate ground is against code.The reason it's not a good idea is with two ground paths any overvoltage can find it's way back through your equip.isolated ground.Also two ground potentials is the biggest source of ground loop hums ect.Unless you had a separate service feed from the utility transformer and panel grounded to a new rod for your audio circuits the best way to handle your grounding is to suplement your existing service ground with an 8' electrode driven at least 6' from any existing rod and connected in parallel not series to the same lug on the grounding/neutral bar in your panel.Have the electrician connect your new circuits isolated ground wire as close as possible to this point and you will have a star grounded low impedence ground path.This is what I did and the noise floor is much lower....Good luck!
- ...