I would like you to also give an example where the branch circuit wiring is #14 gauge wire which would be a more real world example for the majority of homes in the US where guys are plugging their audio systems into a 15 amp convenience outlet circuit in the living room or a den.The resistance of 100 feet of 14 gauge wire, corresponding to a 50 foot run, is about 0.25 ohms. For the 30 amp current spike I hypothesized, that would result in a voltage drop of 0.25 x 30 = 7.5 volts. A 75 foot run would increase that by 50%, to 11.25 volts.