Just how much of a no-no is this? ARC goes as far to print in their manual to say to have the amp and preamp on their own circuit. I live in an apt. and I'm forced to have both plugged into the same outlet. Cords just don't reach....How much sound quality is lost by doing this? It sounds great as is, but is there a major detriment to this? I'm curious.
audiolover718
Post removed 
Jim, you do not understand, Krell runs 30 amp braker on every krell 700cx, 750mcx amp there at the factory, BTW, I have 4 fuses, well with-in the current capability useing a 30 amp breaker, as I said befor, I am not useing all the 30 amps!,however, This amp in particular spikes well above 20 amps while in use, maybe you should call krell, then you will get all the theory as to why this works properly you want, remeber, this amp at full power is 6,000 watts!
Help me Jim or Al, I don't know if my math is right, but isn't 6,000 watts equal to 50 amps on a 120 VAC line?
John, yes your math is of course correct. And the 700cx does indeed have a max power consumption spec of 6000 watts, which if anything seems a bit low in relation to its specified output power rating of 2800 watts/channel into a 2 ohm load (the 8 ohm and 4 ohm ratings being 700 and 1400 watts respectively).

But it seems safe to assume that it would be an unusual occurrence for the amp to be used in a manner that would require it to draw more than 20 amps x 120 volts = 2400 watts for a long enough time to cause a 20 amp breaker to trip.

Best regards,
-- Al
50 amps is correct.

But we should keep in mind that the amp is likely never going to produce such power, as it would only be possible if the load were one ohm. I remember the Apogee Full-Range speaker approached that value, but the speaker cables used in such an installation would add to the load impedance and limit the possibility of such power.

On most 4 ohm loads the output power is about 1500 watts.

In addition if I recall correctly, its the power transformer in that amp that has that rating, not the amp itself. The transformer would current-limit the amp even if the output section was capable of delivering such power.

Line voltage sag can cause some amps to heat up as the bias point can shift somewhat depending on the design so I can see that reducing the sag with a higher current breaker might have an effect. But installing such a breaker without upgrading the associated wiring would be foolhardy and would not meet code in any state in the country.