Audiolabyrinth,
Krell chose to use a 125V 15 amp plug on the unit because the 125V 15 amp duplex is the standard wall receptacle found in dwelling units, homes, in the US and Canada. Krell did choose to use the 15 amp plug for economic reasons. Not because of the price of the 15 amp plug verses a 20 amp or 30 amp plug, but because how many people in the US or Canada have NEMA 5-20R 125V 20 amp duplex receptacles in their living room, family room, parlors, libraries, dens, bedrooms, or recreation rooms? They have 15 amp duplex receptacles because NEC Code says the minimum wire size that can be used on a 15 amp branch supplying power to a 15 amp branch circuit is #14 awg wire connected to a 15 amp breaker. You will find in most cases, at least in the US, residential dwelling units are wired to NEC Code bare minimum standards.
But wait, Krell says the minimum circuit ampacity required for the Krell 700cx amp is 20 amps. Does your Krell 700cx amp have a 20 amp plug on the end of the cord? No, not by what you have said in your last post, it has a 15 amp plug. So why didn't Krell at least install a 20 amp plug on the end of the cord? Well that's easy, any fool knows a 20 amp plug will not fit, plug, into a 15 amp receptacle. Of course if Krell had installed a 20 amp plug on the end of the cord that would have required a 20 amp receptacle with #12 awg cu wire minimum, connected to a 20 amp breaker. Only a 20 amp breaker!
I asked you in my last response to you if the Krell 700cx amp is UL and or CSA Listed. My guess it is not!
As for what Chris Vanhause of Vh-Audio may have told you, I only have your side of the conversation. I would hope Chris is not telling customers it is ok to connect the furutech FI-50 Rhodium plug and Furutech receptacle to a 30 amp circuit.I suggest the manufacture of the plug and receptacle should be contacted and ask them what they have to say. IF, Furutech plugs and receptacles are UL and or CSA Listed connecting them to a branch circuit voltage or amperage circuit other than what the plug and receptacle is designed and manufactured for voids the UL Listing of the device. I would bet it also voids the manufacture warranty.
As for differences found between a 125V 15 or 20 amp plug and receptacle and that of a 30 amp receptacle I suggest you go to the local electrical supply house or Home Depot store in your area and compare them to one another.
What you will find is the 30 amp plug and receptacle contacts are about 50% bigger. Yes more surface area as well as more meat on the bone. After all the devices are designed and manufactured to handle 50% more load than the 15 or 20 amp device.
The spacing between the contacts apart from one another is greater on the 30 amp than the 15 or 20 device.
Here is some more info on the Krell 700cx amp.
Audio Video Revolution, review.
The Stereo Times, review.
I found this thread on AA.
Two 4KVA toroidal transformer in the Krell 700CX?
When connected to a 30 amp branch circuit breaker the only thing that holds that puppy back is the breaker on the back panel of the unit. I wonder if it is a 30 amp? I doubt it.
Audiolabyrinth, is it true the amp has two 4KVA power transformer?
Do you know the ampere rating of the circuit breaker mounded in the back rear panel of the amp? 15 amp? 20 amp? Do you know if it is a magnetic trip breaker only?
Another Agon thread.
.
.
I will leave you with this.
Electrical Forensics
So a 20 amp receptacle installed on a 30 amp breaker could be 135% overloaded for up to an hour before it is supposed to trip open.
30 amps X 135% = 40.5 amps
Has to trip open if overloaded by 200% in 2 minute.
30 amps X 200% = 60 amps
Compared to,
20 amp breaker X 135% = 27 amps.
20 amp breaker X 200% = 40 amps
.
Jim
Krell chose to use a 125V 15 amp plug on the unit because the 125V 15 amp duplex is the standard wall receptacle found in dwelling units, homes, in the US and Canada. Krell did choose to use the 15 amp plug for economic reasons. Not because of the price of the 15 amp plug verses a 20 amp or 30 amp plug, but because how many people in the US or Canada have NEMA 5-20R 125V 20 amp duplex receptacles in their living room, family room, parlors, libraries, dens, bedrooms, or recreation rooms? They have 15 amp duplex receptacles because NEC Code says the minimum wire size that can be used on a 15 amp branch supplying power to a 15 amp branch circuit is #14 awg wire connected to a 15 amp breaker. You will find in most cases, at least in the US, residential dwelling units are wired to NEC Code bare minimum standards.
But wait, Krell says the minimum circuit ampacity required for the Krell 700cx amp is 20 amps. Does your Krell 700cx amp have a 20 amp plug on the end of the cord? No, not by what you have said in your last post, it has a 15 amp plug. So why didn't Krell at least install a 20 amp plug on the end of the cord? Well that's easy, any fool knows a 20 amp plug will not fit, plug, into a 15 amp receptacle. Of course if Krell had installed a 20 amp plug on the end of the cord that would have required a 20 amp receptacle with #12 awg cu wire minimum, connected to a 20 amp breaker. Only a 20 amp breaker!
I asked you in my last response to you if the Krell 700cx amp is UL and or CSA Listed. My guess it is not!
As for what Chris Vanhause of Vh-Audio may have told you, I only have your side of the conversation. I would hope Chris is not telling customers it is ok to connect the furutech FI-50 Rhodium plug and Furutech receptacle to a 30 amp circuit.I suggest the manufacture of the plug and receptacle should be contacted and ask them what they have to say. IF, Furutech plugs and receptacles are UL and or CSA Listed connecting them to a branch circuit voltage or amperage circuit other than what the plug and receptacle is designed and manufactured for voids the UL Listing of the device. I would bet it also voids the manufacture warranty.
As for differences found between a 125V 15 or 20 amp plug and receptacle and that of a 30 amp receptacle I suggest you go to the local electrical supply house or Home Depot store in your area and compare them to one another.
What you will find is the 30 amp plug and receptacle contacts are about 50% bigger. Yes more surface area as well as more meat on the bone. After all the devices are designed and manufactured to handle 50% more load than the 15 or 20 amp device.
The spacing between the contacts apart from one another is greater on the 30 amp than the 15 or 20 device.
Here is some more info on the Krell 700cx amp.
Audio Video Revolution, review.
The Stereo Times, review.
I found this thread on AA.
Two 4KVA toroidal transformer in the Krell 700CX?
When connected to a 30 amp branch circuit breaker the only thing that holds that puppy back is the breaker on the back panel of the unit. I wonder if it is a 30 amp? I doubt it.
Audiolabyrinth, is it true the amp has two 4KVA power transformer?
Do you know the ampere rating of the circuit breaker mounded in the back rear panel of the amp? 15 amp? 20 amp? Do you know if it is a magnetic trip breaker only?
Another Agon thread.
09-13-10: Mclsound
thanks guys
Seems like most are using a 20amp rec. with 10awg wire and 30amp breaker.
.
.
I will leave you with this.
If a circuit breaker is over loaded to a value of 135% it rated current, it must trip within one hour.
If a circuit breaker is over loaded to a value of 200% it rated current, it must trip within two minutes.
Electrical Forensics
So a 20 amp receptacle installed on a 30 amp breaker could be 135% overloaded for up to an hour before it is supposed to trip open.
30 amps X 135% = 40.5 amps
Has to trip open if overloaded by 200% in 2 minute.
30 amps X 200% = 60 amps
Compared to,
20 amp breaker X 135% = 27 amps.
20 amp breaker X 200% = 40 amps
.
Jim