Edit post, 03-09-15: Jea48.
So if the branch circuit feeding the amp is 30 amps, what if there is a ground fault event anywhere in the 120Vac power wiring inside the amp, including the hot side fed of a primary winding of one of the 4kva transformers, to the safety equipment grounded metal chassis of the amp? Will the ground contacts of the plug/wall receptacle combo be able to handle the ground fault current that will travel back to the source, the electrical panel? If the receptacle and plug are NEMA 30 amp rated and UL and or CSA Listed then yes the equipment ground contacts of the plug and receptacle will be able to handle the possibly extremely high current the 30 amp breaker can supply until it reacts to the ground fault load current placed on it and hopefully trips open and breaks the ground fault circuit.
If it's a NEMA 5-15P plug/5-20R receptacle connection who knows? Not the manufacture of the devices. Not UL or CSA.
And I would be willing to bet Krell doesn't know either.
Quote
"Will the ground contacts of the plug/wall receptacle combo be able to handle the ground fault current that will travel back to the source, the electrical panel?"
It should have been obvious but I should have included the plug/wall receptacle Hot contact connection as the Hot brach circuit conductor that is connected to the Hot contact of the receptacle is feeding the high current, caused by the ground fault event, back to the source, the electrical panel, through the safety equipment grounding conductor. "Houston, we have ignition!"
Also in case it was not clear my load calculations, in the post, were for possible FLA full load of the two 4 KVA power transformers. I have no idea what the actuals loads could be. If Al couldn't figure them out from the Krell specs given, I assure you I can't. I did try to find a wiring diagram for the amp on the net without any luck.
03-09-15: Ct0517 post reminded me again from a previous post of his the rear panel 50 amp breaker has a pair of wires for hard wire remote control of the breaker. Just a guess, and that's all it is, the 50 amp breaker has a shunt trip solenoid that when energized will mechanically trip the breaker open. The shunt trip circuit could be controlled through relay contacts of relays that are controlled from each channel of the amp. This could be part of overload protection for the two power amplifiers of the amp. A wiring diagram of the amp's overcurrent protection would be nice.
For those interested,
a look inside the Krell 700CXIt's just a shame Krell did not put a 30 plug on the end of the power cord to began with