asp307 said:
It was recommended to me by a US producer of speakers/cables to ground to the earth using rods and to use a twisted pair for the connection between the breaker and the outlet.
Send him a copy of this.
Quote from Link below:
>>
"Grounding Myths
From Henry W. Ott’s big new book "Electromagnetic Compatibility Engineering"
3.1.7 Grounding Myths
More myths exist relating to the field of grounding than any other area of electrical engineering. The more common of these are as follows:
1. The earth is a low-impedance path for ground current. False, the impedance of the earth is orders of magnitude greater than the impedance of a copper conductor.
2. The earth is an equipotential. False, this is clearly not true by the result of (1 above).
3. The impedance of a conductor is determined by its resistance. False, what happened to the concept of inductive reactance?
4. To operate with low noise, a circuit or system must be connected to an earth ground. False, because airplanes, satellites, cars and battery powered laptop computers all operate fine without a ground connection. As a mater of fact, an earth ground is more likely to be the cause of noise problem. More electronic system noise problems are resolved by removing (or isolating) a circuit from earth ground that by connecting it to earth ground.
5. To reduce noise, an electronic system should be connected to a separate “quiet ground” by using a separate, isolated ground rod. False, in addition to being untrue, this approach is dangerous and violates the requirements of the NEC (electrical code/rules).
6. An earth ground is unidirectional, with current only flowing into the ground. False, because current must flow in loops, any current that flows into the ground must also flow out of the ground somewhere else.
7. An isolated AC power receptacle is not grounded. False, the term “isolated” refers only to the method by which a receptacle is grounded, not if it is grounded.
8. A system designer can name ground conductors by the type of the current that they should carry (i.e., signal, power, lightning, digital, analog, quiet, noisy, etc.), and the electrons will comply and only flow in the appropriately designated conductors. Obviously false."
Henry W. Ott
/////
Posted by Speedskater:
Dedicated Power Line Recommendations - REPRISE! »
>>>>>
asp307 said:
Regarding a twisted pair or standard cable to link the breaker to the outlet, any advantages or is it all about the grounding?
About how long will the branch circuit run be? Don’t forget to figure up, down, and around, when figuring the total length of the run. (2 conductor with ground only! Hot, Neutral, and ground)
The wiring and wiring method used depends on the state and or local electrical code of Pittsburgh, PA. The electrician you hire will know what is code for your town. He will determine what will work for your wiring installation job.
IF NM-B sheathed cable, (Romex is a trade name of), can be used for the electrical wiring installation that works great for audio dedicated branch circuits.
IF because of code or because other reasons it has to be in conduit ask the electrician if MC aluminum armor cable meets code for your town. (2 wire with ground only! Hot, Neutral, and insulated green wire.)
If that meets code make sure he buys solid wire conductors and not stranded wire. Don’t let him talk you out of it. Especially if you want to use #10awg wire. Trust me he will try to get you to use strand wire. If he says nobody has 10-2 with ground solid wire MC AL armor cable tell him to try an electrical wholesale house in town. They will have it.
Worse wiring method for audio branch circuits is for the dedicated branch circuit wires pulled in an empty conduit where they are loose and randomly laying inside the conduit. This method can lead to induced voltage noise on the equipment grounding conductor.
A true dedicated branch circuit does not share a conduit or cable with any other branch circuits.
Example: 10-2 with ground NM-B sheathed cable.
http://www.wireandcabletogo.com/10-2-W-G-NM-B-Wire-Orange-250ft-500ft-or-1000ft-Coil.html?gclid=CP3y...
Example: MC AL armor cable
http://www.southwire.com/products/ARMORLITETypeMCOEM.htm