NFPA is a human protection code; insufficient for transistor protection. Transistor protection both *meets* and *exceeds* those human safety requirements.
Human safety discusses resistance. Transistor safety also addresses impedance and equipotential. NFPA does not discuss the latter two. Because NFPA is only about human protection.
I did. Stated repeatedly in multiple posts. Appliances protection both *meets* and *exceeds* what is required by human protection codes such as NFPA.
IEEE defines how to exceed those codes. IEEE say why ’whole house’ protection is 99.5% to 99.9% effective. Plug-in protectors have no earth ground - maybe add another 0.2% protection. None of that contradicts what is good earthing for human protection and remains insufficient for appliance protection.
More quotes from various IEEE sources:
Martzloff’s 1994 IEEE paper says same about impedance because a protector (SPD) is only as effective as its earth ground:
An IEEE guide shows a protector, connected to a wall receptacle safety ground, earthing an 8000 volt surge destructively through a nearby TV. That protector was not connected low impedance to earth ground; was too close to and therefore damaged a nearby appliance. Again, protection defined by impedance - a short connection to earth. Protection not provided by a wall receptacle safety ground - that has low resistance and high impedance.
That same guide defines earthing that must exceed NFPA requirements:
Low impedance connection to single point earth ground is why the Cutler-Hammer and Leviton ’whole house’ protectors are so effective. With numbers (ie 50,000 amps) that define protection from direct lightning strikes. Because a protector is only as effective as its earth ground - including a low impedance connection.
Also critical is inspecting the ’primary’ surge protection layer - that is ignored by NFPA and NEC.
Human safety discusses resistance. Transistor safety also addresses impedance and equipotential. NFPA does not discuss the latter two. Because NFPA is only about human protection.
First you need to start with what is the intention of the National Electrical Code.
I did. Stated repeatedly in multiple posts. Appliances protection both *meets* and *exceeds* what is required by human protection codes such as NFPA.
IEEE defines how to exceed those codes. IEEE say why ’whole house’ protection is 99.5% to 99.9% effective. Plug-in protectors have no earth ground - maybe add another 0.2% protection. None of that contradicts what is good earthing for human protection and remains insufficient for appliance protection.
More quotes from various IEEE sources:
It is important to ensure that low-impedance grounding and bonding connections exist among the telephone and data equipment, the ac power system’s electrical safety-grounding system, and the building grounding electrode system. ..Failure to observe any part of this grounding requirement may result in hazardous potential being developed between the telephone (data) equipment and other grounded items that personnel may be near or might simultaneously contact.Low impedance - not low resistance.
Martzloff’s 1994 IEEE paper says same about impedance because a protector (SPD) is only as effective as its earth ground:
An effective, low-impedance ground path is critical for the successful operation of an SPD. ... Therefore, an evaluation of the service entrance grounding system at the time of the SPD installation is very important.
An IEEE guide shows a protector, connected to a wall receptacle safety ground, earthing an 8000 volt surge destructively through a nearby TV. That protector was not connected low impedance to earth ground; was too close to and therefore damaged a nearby appliance. Again, protection defined by impedance - a short connection to earth. Protection not provided by a wall receptacle safety ground - that has low resistance and high impedance.
That same guide defines earthing that must exceed NFPA requirements:
To achieve optimum overvoltage protection, the connecting leads between the SPDs and the panel or protected equipment should be as short as possible and without sharp 90-degree bends.90 degree bends and long wires (ie more than 10 feet) increase impedance (but not resistance). Therefore reduce appliance protection. NEC defines human protection; not appliance protection. Unfortunately electricians, who are taught code, are not taught concepts such as counterpoise, equipotential, and impedance. Concept necessary to upgrade earthing for surge protection.
Low impedance connection to single point earth ground is why the Cutler-Hammer and Leviton ’whole house’ protectors are so effective. With numbers (ie 50,000 amps) that define protection from direct lightning strikes. Because a protector is only as effective as its earth ground - including a low impedance connection.
Also critical is inspecting the ’primary’ surge protection layer - that is ignored by NFPA and NEC.