Rega Isis cd player ......Dedicated 20 amp circuit?


I just bought a Rega Isis cd player and noticed it has a 20 amp power cord. Do i need a dedicated 20 amp circuit for this player? 
tattooedtrackman
Looking at photos of the rear of your cd player, it does not have the 20A male IEC power cord receptacle. The pin pattern for a 20A cord is different than a 15A cord. What makes you think you have a 20A cord?   
I have a REGA ISIS Valve spinner .... it is built like a tank at > 45 lbs in weight with a massive power supply.

Absolutely no need for a 20 amp dedicated feed (unless you feel compelled to install one for ??....): a "standard" 15 amp dedicated power line like I have. is perfectly fine.
dill I was looking at the Rega Reference power cable web page and specifications say....Power lead cable rating 20 amp.. Thats why i thought i needed a dedicated 20 amp circuit. But akg_ca answered my question 
As far as I know, from the installation cost perspective, there's no difference between running a dedicated 20 amp line and a 15 amp line from the breaker box. It just gives you the option to use the wall plug in the future for a high current amp.