Replacing generic RECEPTACLES


How important is it to replace your generic receptacles with audio grade receptacles . I already replaced my stock power cords to high end Shunyatas. Would it still be necessary to still change my generic receptacles to audio grade? 
128x128Ag insider logo xs@2xtattooedtrackman
@tattoo, just so I understand, the 20A dedicated line is installed with 2 duplex receptacles. 20 amps would require commercial receptacles. Is this correct?

Does a receptacle and 15 amp line already exist for your CDP?
In any event, you will be adding the Furutech and I assume running new 12 gauge Romex to a 20A breaker at the circuit panel.
Make sure your electrician installs the ground wires from both dedicated lines to the Ground Bar in the circuit panel.

lowrider57......The 20A dedicated line right now that my electrician installed with 2 duplex receptacles says TR . They are white. I dont know what you mean by commercial. From what i found on line TR stands for taper resistant and sell for $3.50 ea.Very cheap and prob garbage for audio. Right now im using that for my amp and preamp until my 2 Furutech GTX -d r come in the mail and will replace the TRs. Also right now my CDP is on a non dedicated 15A. And waiting for the 20A Furutech GTX-d r to come also in the mail , then i will have my electrician run the dedicated 20A line and put in the Furutech for my CDP and have him replace the 2 cheap duplex TRs and install the 2 Furutechs for the amp and preamp.
@lowrider57 .........I will tell the electrician about what you said about installing the ground wires from both dedicated lines to the Ground bar in the circuit panel.. I dont know what you mean by that but i will tell him. 
OK, I've got it now. It sounds like a solid plan.
Running both lines to the ground bar in the panel means that they will share the same ground, less chance of a ground-loop.

Please let us know how it all comes together. You have great components.

lowrider57
Running both lines to the ground bar in the panel means that they will share the same ground, less chance of a ground-loop.
This is required by NEC in the US. All grounds must be connected to the ground bus at the service panel.