tomfoolery...... Thats what i would have done if i already had a 15A dedicated line. Since i do not , I will just put a 20A dedicated line in for my CDP and the 20A Furutech.
- ...
- 321 posts total
tomfoolery And yes, you can replace a 15 amp outlet with 20 amp one. It makes thing safer!You can replace a 15A outlet with a 20A outlet provided the wire connecting the outlet to the panel is of the gauge specified under the NEC and your local code for a 20A circuit. Otherwise, you have a code violation and a definite safety hazard. And there is nothing inherently "safer" about a 20A line compared to a 15A line. If they are each properly installed, they are of equal safety. |
Possibilities are endless: How about replacing your 12-3 nomex from the panel to the receptacle with some exotic wire? Maybe the circuit breaker itself on the dedicated line should be replaced with a high end breaker. Also, isolating (not touching the other wires) the power line between the panel/breaker and the dedicated receptacle would eliminate the possible interference from the other circuit lines (microwave, refrigerator, etc,). To totally eliminate the vibration issues originating from the framing of the dwelling, one can encase the dedicated line in a foam filled solid conduit (not sure if this complies with national electrical codes). ;-) |