stereo52,661 posts01-21-2019 6:16pm
I don’t believe anyone commenting here is a licensed electrician for your area nor knows your areas electrical codes. I would trust your licensed electrician before any of us. While everyone is trying to be helpful, we are merely speculating at best. If everyone got to you and you are truly worried, have a different licensed electrician come by to look at everything for a second opinion. It will be money well spent for your piece of mind.
I will bet you the AHJ in Chicago does not allow the equipment grounding conductor of an IG receptacle to be connected to an isolated earthed ground rod as the OP described the electrician did it.
OP said:
The other 20 amp outlet is grounded directly from the outlet to the outside rod with a clamp that is attached to the rod itself, I saw that with my own eyes. It is a straight wire that goes from the outlet to the outside and has nothing to do with the inside panel or anything else in the house.
OP said:
What is the difference between the ground wire that is connected to the panel itself and the one that goes to the outside, it still goes thru the panel but it is not attached to the panel itself it just goes thru the pipe that goes outside where the meter is and from there it is attached to the rod.
//
2014 NEC® section 250.146 Connecting Receptacle Grounding Terminal to Box
(D) Isolated Ground Receptacles
Where installed for the reduction of electrical noise (electromagnetic interference) on the grounding circuit, a receptacle in which the grounding terminal is purposely insulated from the receptacle mounting means may be permitted. The receptacle grounding terminal shall be connected to an insulated equipment grounding conductor run with the circuit conductors. This equipment grounding conductor shall be permitted to pass through one or more panel boards without a connection to the panel board grounding terminal bar as permitted in 408.40, Exception, so as to terminate within the same building or structure directly at an equipment grounding conductor terminal of the applicable derived system or service. Where installed in accordance with the provisions of this section, this equipment grounding conductor shall also be permitted to pass through boxes, wireways, or other enclosures without being connected to such enclosures
http://www.cooperindustries.com/content/dam/public/wiringdevices/BuyersGuides/AHBG/I/AHBG-I-09.pdfWording is word for word right out of 2014 NEC, page 70-133.
Nothing said about connecting the equipment grounding conductor to a ground rod.
I see no NEC exception given for the OP’s electrician. I also doubt the Chicago AHJ would approve what the guy did either. It’s dangerous! Surely you would agree?
AS for the OP getting another electrician out to house I agree he should. First thing he should do is land the IG equipment grounding conductor on the ground bar in the service electrical panel where it should have been landed in the first place. Then the OP should have the electrician inspect the rest of the work the other guy did.
.