The Audience wire is interesting, but I would actually just use cryo'd 10awg Romex myself. VH Audio sells cryo'd 10-2 Romex for 2.99/foot, or $469 for a 250 foot roll. The Romex will meet code for running inside walls and through attic areas. Other wire may or may not (and might have to be run in conduit). Some people have said they get better results with 8awg THHN, but that is going to be stranded and also needs to be run completely in a conduit. The Romes is solid core, which is better in my opinion (even if it doesn't quite have the current cabability of 8 awg). |
Post removed |
Under the electrical code https://www.usawire-cable.com/pdf/nec-ampacities.pdf 14ga wire is good for 20A, 8 for 40A. Continuous. Other than large Class A amplifiers, 4 nines of HiFi systems don't ever come anywhere near even 20A. With a linear supply, that's ≈1400W. |
https://www.usawire-cable.com/pdf/nec-ampacities.pdfJust one example why the NEC should never be used as a design specification or an instruction manual. The NEC is bare minimum electrical safety standards. NEC 90.1: National Electrical Code 90.1 Purpose:FPN, Fine Print Notes. Suggestions, not mandatory. Continuous..... Average..... Doesn’t account for dynamic peaks, spurts, of current draw from an amplifier when amplifying a high dynamic signal. Amplifier power supplies like, need, a steady AC mains Line voltage. Nelson Pass https://www.passlabs.com/press/power-supplies-commentary-consumers Post by Ralph - Manufacturer, Atma-Sphere Music Systems https://www.audioasylum.com/audio/cables/messages/17/174988.html The subject matter is for a power cord. The same would hold true for branch circuit wiring. Even more so for a convenience outlet branch circuit where other loads are connected to the same circuit as an audio system. Jim . |
@jea48 The breaker limits the current below the wire ampacity. A 15A circuit has 5A current reserve capacity in the wire according to the NEC. From Pass: Typically, a Class AB stereo amplifier rated at 200 watts per channel continuously should be capable of delivering 700 watts or so, and this means a transformer rating of about 2000 watts. Anything less means non-continuous operation. This might be alright for a class AB amplifier where maximum continuous operation is not required.Confirms that most systems do not require 20A. Any humongo transient that occurs when the 120v line is 0v is going to suck down the caps regardless of the transformer size. The supply capacitors need to be of sufficient capacity and low ESR to handle the transients supplying the required current without falling below the required voltage. Toroids are somewhat fan-boy sales bait. They are not a free lunch. http://www.soundstagenetwork.com/maxdb/maxdb071998.htm I'd read Ralph's post and agree with him. |
- 36 posts total