@theo
Both Line 1 (L1) and Line 2 (L2) alternate down each side of the panel. That’s how 240V load(s) can be fed from a 2 pole breaker.
Example:
Left side... Right Side
L1 .................. L1
L2 .................. L2
L1 .................. L1
L2 .................. L2
With that said the electrician may very well have fed the two 120V branch circuits from both Line 1 and Line 2. Easy way to check is with a multimeter. If both the circuits are fed from opposite Lines, legs, measuring from the hot contact (smaller slot) of a receptacle connected to one of the branch circuits to the hot contact of a receptacle connected to the other branch circuit you will measure 240V nominal. If both circuits are fed from the same Line,leg, you will measure 0 nominal volts.
You say an electrician installed the two circuits a number of years ago. Do you remember if the electrician installed Romex? Did he install two Romex cables or maybe only one?
IF only one Romex cable he installed a 120/240V 3 wire multiwire branch circuit. If that is the case you have two separate 120V circuits that share a common neutral conductor. The Romex cable will have 3 insulated conductors + a bare equipment grounding conductor.
If it is a multiwire branch circuit both hot separate circuit conductors must be fed from breakers fed from L1 and L2.
.
Both Line 1 (L1) and Line 2 (L2) alternate down each side of the panel. That’s how 240V load(s) can be fed from a 2 pole breaker.
Example:
Left side... Right Side
L1 .................. L1
L2 .................. L2
L1 .................. L1
L2 .................. L2
With that said the electrician may very well have fed the two 120V branch circuits from both Line 1 and Line 2. Easy way to check is with a multimeter. If both the circuits are fed from opposite Lines, legs, measuring from the hot contact (smaller slot) of a receptacle connected to one of the branch circuits to the hot contact of a receptacle connected to the other branch circuit you will measure 240V nominal. If both circuits are fed from the same Line,leg, you will measure 0 nominal volts.
You say an electrician installed the two circuits a number of years ago. Do you remember if the electrician installed Romex? Did he install two Romex cables or maybe only one?
IF only one Romex cable he installed a 120/240V 3 wire multiwire branch circuit. If that is the case you have two separate 120V circuits that share a common neutral conductor. The Romex cable will have 3 insulated conductors + a bare equipment grounding conductor.
If it is a multiwire branch circuit both hot separate circuit conductors must be fed from breakers fed from L1 and L2.
.