To Fuzztone: Dunno, maybe. The electrician installed them when I built my home. They have their own grounding rod.
"Their own grounding rod"...
@
output555,
Any idea how the electrician wired the new ground rod to your 4 dedicated 20 amp audio outlets?
Is that one 20 amp dedicated branch circuit with four 20 amp outlets, (two duplex receptacles), connected to the one branch circuit?
1) Did the electrician only connect the ground wire from the dedicated, isolated, ground rod to the duplex receptacles equipment ground terminal, therein not using the dedicated branch circuit wiring equipment grounding conductor for the primary safety equipment ground?
Or
2) Did the electrician connect/splice the dedicated ground rod ground wire to the 20 amp dedicated branch circuit wiring equipment grounding conductor, and from the same connection/splice use a grounding pigtail that connects to the ground terminal of each duplex receptacle?
IF the electrician only wired the new dedicated, isolated, ground rod as I described in 1) not only is that electrically dangerous it can also cause noise on audio equipment that use the safety equipment grounding conductor. Is that the source of your radio station RFI? Probably not.
(Note: It only takes one piece of audio equipment, that uses the safety equipment ground, to connect all the chassis of all connect pieces of audio equipment by wire interconnects.)
FYI, lightning especially loves dedicated, isolated, ground rods that are not bonded, connected, to the main electrical service earth grounding system. Therein the electrical service Grounding Electrode System.
/ / / /
Just curious, what type of branch circuit wiring did the electrician install?
Example 2 wire with ground Romex cable? (NM cable)
Other?
.