If you say you have a dedicated line and are getting noise from the AC then you dont have a true dedicated line. A true dedicated has to be brought in independent from the street. At the very least you are sharing a ground on your dedicated line.
A true dedicated has to be brought in independent from the street.
Good luck getting that...
At the very least you are sharing a ground on your dedicated line.
Per code the EGC (Equipment Grounding Conductor) of a branch circuit shall be ran in the same conduit or cable and connect the equipment ground bus in the same panel the branch circuit originates.
Exception, when a branch circuit is fed from a subpanel where an isolated ground receptacle is used an insulated isolated ground EGC can be extended and connected to the main electrical panel equipment ground bus.
No dedicated isolated ground electrodes allowed... They serve no purpose and can be electrically dangerous to life.
An Auxiliary ground rod is acceptable per NEC provided it is connected to the EGC of the branch circuit wiring. (NEC 250.54)
.