I took the time this morning to look up the unit, I believe, you are buying. Its wiring scheme is different than the 3000W unit video above.
Here is the manual for this 2000W unit. (Click on the Link below.)
https://www.renogy.com/content/RNG-INVT-2000-12V-P2/INVT-P2-Manual.pdf
Page 8 shows a ground lug (4)
Page 11.
Grounding
The Renogy Pure Sine Wave inverters come equipped with a grounding lug to appropriately ground to earth or to another designated ground (for example, a metal frame of an RV). The connections to ground must be tight and against bare metal. Whether using the inverter in a
mobile application, such as an RV, or in a building, grounding is highly recommended. The recommended wire size for grounding is 10 AWG insulated copper strand wire. For more
information regarding grounding, users and/or installers must consult with the Local and National Electric Codes (NEC) for more specific grounding regulations and suggestions as they can change per scenario.
This applies for your situation.
Local and National Electric Codes (NEC) for more specific grounding regulations and suggestions as they can change per scenario.
Do not run the #10awg ground wire to a dedicated outdoors ground rod. The ground wire needs to connect the electrical service grounding system of your house.
Where to connect the #10awg ground wire? I would need more information.
.