I ran two circuits to my system, one on each leg. I do keep my system all on the same leg and plug other things into the other leg but that is really just a local thing.
What type of wiring method did you use?
Did you install a 3 wire 120/240V multi wire branch circuit consisting of two Hot conductors, one common shared neutral conductor, and one EGC (Equipment Grounding Conductor)?
If yes, only the unbalanced load current of (L1) to neutral and (L2) to neutral will return on the neutral conductor back to the source. The balanced load of (L1) to neutral and (L2) to neutral are in series with one another and are fed by 240V, nominal.
Here is a good example of how a 3 wire multi wire circuit works.
(Imagine the transformer’s split phase secondary winding is 120/240V)