@jea48
Do you normally specify isolated ground and is that why you recommend MC?
New Electrical Circuit
I have an older house with open circuits so I am wiring a new dedicated circuit for my audio gear. Before I do so, would it be very advantageous to bump up the quality of the outlet and / or wiring to improve quality or is this overkill? Has anyone done this in the past and what would you recommend?
@jea48 Do you normally specify isolated ground and is that why you recommend MC? |
For a residential house I never recommend an isolated ground. It would not serve any purpose what so ever. FYI even in commercial and industrial facilities an IG, Isolated grounding conductor and IG type outlet are seldom used now days. They where big in the 1970s, 80s and 90s. They started fading in the early 2000s. I recommend 2 wire solid copper aluminum armor MC cable. Example: 10/2 Solid copper Aluminum armor MC (Metal Clad) Cable The reason I like MC cable better than Romex is because of the way it is constructed. Hot, neutral, and insulated green equipment grounding conductors are tightly twisted together in a spiral twist and held tightly together by the armor. MC cable NOT AC cable (commonly called BX). AC cable is garbage for feeding audio equipment. Romex is ok provided care is taken when installing it. Avoid twisting the cable as not to change, distort, the lay of the EGC (Equipment Grounding Conductor) between the Hot and neutral current carrying conductors. That’s next to impossible to do. If you tell the electrician to install the Romex keeping the cable flat without any twists. He will think you are nuts... Read pages 12 and 13. Note the chart on page 13. Integrating Electronic Equipment and Power . |
@jea48 My electrical box is outside. Can they encase the (Southwire Armorlite 125-ft 10/2 Solid Aluminum MC (Metal Clad) Cable) inside metal conduit for the outside portion for weather proofing? |
Not really. The electrician can use a, (example), EMT to AC/MC/FMC/NM Transition Fitting . He will remove the aluminum armor for the length of the EMT conduit and the wire needed for make up in the electrical panel. Or he can use a junction box inside to transition from EMT conduit box connector to an MC cable box connector. I think the EMT to MC transition fitting would work better, jmho. Your electrician on the job site will know what will work best for him for his install situation. If you decide to have MC cable installed make sure the electrician installs 3/8" anti-short bushings on all cut MC armor ends. Anti-short bushings are not required by NEC code. Have him install them anyway... They protect the insulation on the conductors from the sharp edge of the armor. . |