Belden tech support replied to my email and said they recommend their FPLP cable (83802, 83803, etc.) not be used for 110v power supply, from panel to receptacle. They said it is for "Control and Instrumentation" cables for Fire Alarm and Tray applications and are not designed for 110v applications.
The assistant state electrical inspector and regional offices both said an emphatic "NO" when I asked if FPLP can be used in this manner. I have now contacted three electricians, the regional and state electrical inpectors offices, and Belden tech support. They all give the same answer.
I had hoped 83803, at least, could be approved but unless it was overlooked by the local inspector it would not be, not in my state. I was told I'd have to get it all removed at whatever phase of construction it was discovered. That could prove to be a very costly mistake.