11-12-14: CtsoonerMatt, I would advise against this, if I am correctly interpreting that what is being recommended is running outlet grounds to an earth connection other than the one that grounds the service panel. If that is not a correct interpretation of what is being suggested, I'm sure the others will clarify further.
I'd recommend for your electrical is to have totally separate and grounded (to earth) circuits for EACH outlet. I did that and it makes a huge difference.
11-12-14: Agear
I too have dedicated lines with with isolated earth (ionic) grounds.
See section 1.2 on pages 7 and 8 of this paper by Bill Whitlock of Jensen Transformers, who is a renowned expert on such matters. Note the concluding sentence: "If multiple ground rods are used, Code requires that they all MUST be bonded to the main utility power grounding electrode." Also note the section starting at the bottom of page 3, "myths about earth grounding and wires."
As explained in section 1.2 of the paper, having earth connections for the system that are separate from that of the main service panel is a code violation, a shock hazard and a fire hazard in the event of an equipment fault, and a hazard to the equipment (or worse) in the event of a nearby lightning strike. And I'll add that it would also be a potential excuse for your insurance company to not pay in the event of one of these disasters.
You may want to start a separate thread on the subject of AC wiring and grounding, which will probably catch the eye of Jea48 (Jim), who is our leading expert here on such matters.
Regards,
-- Al