I already have an electrician about to make the change for me......
12-17-09: Rapogee
Rapogee,
You will need a 20 amp branch circuit then. #12 awg wire minimum with a 20 amp breaker.
Just an added note if the breaker trips on occasion due to start-up inrush current of the Krell most electrical panel manufactures make breakers with a longer inrush current lag time.
Here is some info.
Jim