Try running a #14 awg to the outlet that your power conditioner is using, to a cold water pipe and clamp off to that.Tjtrout20,
07-07-11: Tjtrout20
No longer an NEC approved method. Not since 1996 I believe. Too many plumbers were getting shocked or electrocuted.
>>>>>>>>>>>>>>>
This dedicated ground rod for the line conditioner will be about 16 feet away from the ground rod for the electrical wiring for my house.
07-07-11: Tiofelon
Tiofelon,
The dedicated ground rod is a bad idea as others have pointed out. Will not meet NEC code either.....
What NEC will allow for old 2 wire ungrounded receptacle/ branch circuit is to install a new equipment ground wire and connect it to the existing main electrical grounding system, (Grounding Electrode System), of the house.
Look at running a ground wire along the exterior of the house and connect it to the ground wire that comes from the house to the existing ground rod. Use an approved wire connector such as a split bolt. DO NOT cut the main ground wire that runs to the existing ground rod......
You might also be able to run the new ground wire back into the house and connect it to the ground bar you spoke of in a later post.
Wire must be protected from physical damage. Support often.
If it were me I would use a solid #10 awg copper wire.
It would really be best to hire a licensed electrician to do the job......
Method for grounding a non grounded receptacle/branch circuit.
NEC 2008 250.130 (C)
Local code (AHJ) has the final say.