Do not use spades on an A/C outlet, they are not designed for A/C. Spades will stick out too far and might not fit back in the box without breaking. Bob_reynolds is correct about finding better outlets that have flanges that crimp down on the bare wire. Get a hospital grade duplex receptacle like a Hubbell 8200-I, it works fine with 10 ga. Romex.
Spade connectors from Romex to outlet?
Has anyone used spade connectors on the end of their Romex to connect the Romex to the screw down terminal of the outlet? I am switching from 12 gauge to 10 gauge and am having a hard time getting the bigger 10 gauge under the screw. I finally got the wires in there but in this process I started to think - why not use spade connectors on the end of the Romex. Seems like it would be a much better connection. Has any one done this? Which spades did you use? I'm more partial to the spades with screw down (mechanical) connector for the wire. As apposed to the crimp style.
Any input from folks that have been down this road would be appreciate
- ...