Hello again, Jea48: OK, I'll tell my electrician that a 2 pole 70A breaker at the main box is good. When you say that the 2 hots and neutral on the main feed from the house should all be 2AWG copper and the ground should be #6AWG, for a total of 4 individual cables from the house panel to sub-panel? I didn't even realize that the ground wire was supposed to return to connect to the main house panel!!
"The sub panel will have a separate equipment ground bar bonded, connected, to the metal panel enclosure."
What do I know? I thought we were going to run a ground wire from the sub-panel via a #6G bare copper wire to an 8'-10' pole hammered into the ground at least 8' from the garage and that was THE ground... Do I still do that, even with the #6G returning to the main house panel [underground and in the soffit] along with the 2 hots and 1 neutral #2G's? BTW, if I use a PVC tube to encapsulate the underground wires will that be a different type of wire/can it be the same as the "in-house/soffit type" as compared to an "underground feeder cable"? I was checking prices on #2AWG copper cable and we're up to at least $2.50 per foot! Does that mean 65' + 45' = 110'x3 runs (2hot,1neutral) for a total of 330' x $2.50ea = $825 plus the 110' of #6 ground @ $xx? per foot? WOW...
Also, when you say the dedicated branch circuit will have 1hot,1neutral,1gnd... you are referring to the individual wire of 12/2 or preferably 10/2 Romex which attaches to the outlet? When you say "No sharing of neutral" what does this imply? I was thinking of running 2 x 5362 Hubbels next to each other 9for a total of 4 plug in points0 per 20A dedicated line... and I was going to place 3 of these on the wall behind my speakers to hook up all the amps, subs, etc, with therefore 2 add'l outlets per 20A line... Does this work in theory? Thanks for all your help.
"The sub panel will have a separate equipment ground bar bonded, connected, to the metal panel enclosure."
What do I know? I thought we were going to run a ground wire from the sub-panel via a #6G bare copper wire to an 8'-10' pole hammered into the ground at least 8' from the garage and that was THE ground... Do I still do that, even with the #6G returning to the main house panel [underground and in the soffit] along with the 2 hots and 1 neutral #2G's? BTW, if I use a PVC tube to encapsulate the underground wires will that be a different type of wire/can it be the same as the "in-house/soffit type" as compared to an "underground feeder cable"? I was checking prices on #2AWG copper cable and we're up to at least $2.50 per foot! Does that mean 65' + 45' = 110'x3 runs (2hot,1neutral) for a total of 330' x $2.50ea = $825 plus the 110' of #6 ground @ $xx? per foot? WOW...
Also, when you say the dedicated branch circuit will have 1hot,1neutral,1gnd... you are referring to the individual wire of 12/2 or preferably 10/2 Romex which attaches to the outlet? When you say "No sharing of neutral" what does this imply? I was thinking of running 2 x 5362 Hubbels next to each other 9for a total of 4 plug in points0 per 20A dedicated line... and I was going to place 3 of these on the wall behind my speakers to hook up all the amps, subs, etc, with therefore 2 add'l outlets per 20A line... Does this work in theory? Thanks for all your help.