I also bought the optional ISOLATED grounding bar for it.
Why? An isolated ground bar will serve no purpose. I imagine the panel enclosure will be mounted to wood studs and the branch circuit wiring will be NM-B cable. (Romex is an example of NM-B).
How does your electrician plan bonding the panel enclosure to the main electrical systems equipment ground? Is he going to install two equipment grounding conductors from the main electrical panel to the sub panel? One for the isolated equipment ground bar and one for the panel enclosure?
The most serious deviation from all our discussion is that because I'm only running a 70Amp main breaker (into the 125A panel) my electrician and the guys at the electric supply store told me 2G wire is way overkill and that 4G can handle 100A service so I shouldn't waste my $$$ on the 2G and just get the 4G... which, although I was hesitant not to continue with "over-overkill everything"... I decided to do the 4G.
NEC 2005 Table 310.16
#4awg 60 C is good for 70 amps, not 100......
Because of the distance from the main electrical panel to the sub panel I would have stuck with the #2awg minimum.
my electrician and the guys at the electric supply store told me 2G wire is way overkill and that 4G can handle 100A service
The guys at the electrical supply store are not electricians.
Did you ask to see your Electrician's Electrical License?
You are not installing an electrical service. You are installing a feeder and a sub panel. NEC does allow # 4awg for a 100 amp electrical service. But in most cases the service entrance conductors are less than 25 ft.
In your case the larger feeder wire is for voltage drop due to the air conditioning load, small refrigerator, as well as the dynamic demand your audio system's Power Amp/s
may present on the feeder. You want the voltage not to fluctuate with load changes as much as possible.
I also didn't skimp on the ground for it... while everyone told me the ground cable can be one size smaller than the main ones,
I think they confused the neutral, (The Grounded Conductor), with the equipment ground, (The Grounding Conductor).
NEC 2005 Table 250.122 Minimum Size Equipment Grounding Conductors for Grounding Raceway and Equipment.
70 amp breaker - minimum #8 awg copper.
I said go with a #6 but I think for an audio system a larger wire would probably be better.