On one leg or two legs?


If you install two dedication circuits, would you install both breakers on the same leg or one on each? and why?
houstonreef
Ozzy,
They are physically on both sides of the panel, I'm not sure it electrically corresponds to an opposite legs, or not. I will have to check that later tonight.
I tried to plug it into one outlet, stll hums.
I have licenced electrician to install separate panel with five dedicated lines connected to it:
A sub panel fed from the main electrical panel.
By chance do you know what size wire he used to feed the sub panel?

I assume the electrician fed the sub panel from a 2 pole breaker in the main panel. Look on the breaker handle of the breaker what is the number? 40, 50,60, ect?

Because you have a sub panel the panel will have a separate ground bar. The equipment grounding conductors that are part of the dedicated branch circuits that feed the receptacles will terminate on this bar. The ground bar will have an equipment grounding conductor, wire, that goes backs and connects to the main electrical panel ground bar. No exception....per NEC.

He used Romex 12/3 wire, and to my understanding, at least, that's how I asked him to do it, ground wire from each receptacle (actually there are two receptacles on each run of wire)......
A dedicated circuit feeds two duplex receptacles? Is that correct?
Why did you use 12/3 with ground? Is the ground bar in the sub panel an isolated ground bar? There by isolated from the panel's metal enclosure?

...... is connected to a ground bar in the panel, and the ground bar is connected to a copper ground rod right next to the panel, and to a common house ground elsewere.

More than likely here is your problem. Just bet you have a difference of potential, voltage, between the equipment ground at the receptacles and the neutral, the grounded conductor.

Per NEC the feeder equipment grounding conductor shall be installed in the same cable, or raceway, as the feeder current carrying conductors. And the equipment grounding conductor shall terminate in the same panel the feeder is fed from.
http://www.aes.org/sections/pnw/pnwrecaps/2005/whitlock/whitlock_pnw05.pdf
Jea 48,
Sub panel is connected to the main one with 4 AWG wire, with Black, White, Red and naked copper ground conductors.
Breaker in the main panel, feeding the sub panel is 60.
The wire he used for dedicated circuits has Black, White and naked copper ground conductors, so I guess, I mistakingly called it 12/3.
All five dedicated circuits feed 5 duplex receptacles, that is correct.
I don't think, that the ground bar in the sub panel is isolated from the panel metal enclosure.
Yes, sub panel ground bar IS connected to the main panel ground bar.
Also main panel ground bar is connected to an additional
copper rod, installed at the same time, as the sub panel.
And one more thing: I noticed, that a small connector box with TV and Internet cables, has a ground wire, connected to the main panel ground bar.
I have two questions:
1. When evrybody says "isolated ground" does it mean ground bar in the panel isolated from the metal enclosure?
And, if it's not isolated from the panel (like in my case, it seems), would that be a problem causing ground loop?
2. You'd have to forgive me, but I'm not entirely clear about the last part of your post;
"More than likely here is your problem. Just bet you have a difference of potential, voltage, between the equipment ground at the receptacles and the neutral, the grounded conductor.

Per NEC the feeder equipment grounding conductor shall be installed in the same cable, or raceway, as the feeder current carrying conductors. And the equipment grounding conductor shall terminate in the same panel the feeder is fed from".
And how exactly should I correct this problem?
Thanks a lot for taking your time- it's really priceless.
My guess, for what it's worth is that you have multiple ground rods. The two at the main panel are correct...but that one separate, even if connected to the main grounds may be the culprit.