Tim,
Installing an IG recept on an NM-B branch circuit will not have any benefit whats so ever. Using a ferrous metal box in place of the plastic box could actually degrade the sonics of you audio system.
IG receptacles are mainly used in commercial or industrial buildings where EMI/RFI noise may be present on metallic electrical conduits, building steel structures, metal wall studs, ect, ect.
In this case for sensitive electronic equipment a IG recept may be desired.
Lets say a customer bought a piece of equipment that states the equipment must be connected to a 120V 20 amp dedicated circuit with an IG NEMA 5-20R receptacle.
First off to be a "true dedicated" branch circuit the circuit wiring can not share a conduit with any other branch circuit wiring.
So the electrician installs a 1/2" EMT, (thin wall), conduit from the electrical panel to the new recept outlet location. (Distance is short voltage drop is not a problem)
For the wire he selects #12 THHN.
(1)Black conductor, hot.
(1) White conductor, neutral.
(2) insulated green conductors.
** One green wire bonds, connects to the metal rough-in box and the other green wire connects the ground screw terminal on the IG recept.
Back at the electrical panel The black hot connects to a 20 amp breaker. The white wire to the neutral bar. And 99.9% of the time both green equipment grounding wires connect to the same equipment ground bar..... NEC will allow the ground wire that is connected to the IG recept to extend through other upstream panels,(that feed the panel that is feeding the new dedicated branch circuit), and connect the ground wire where the main feeder neutral is connected to earth.... How often do you think that happens?
Now, that I am thinking about it, would actually hooking up the isolated ground correctly possibly help me get rid of the rf noise coming from my furnace ignition??
Simple answer, no....
At this point you can't say for sure the EMI/RFI is being radiated through the air or being carried on your homes wiring... Or Both...
You would of thought the Heating and Air Conditioning Contractor would have at least sent out a tech to make sure the ignitor assembly was firmly connected to the burner assembly. And the burner assembly securely fastened to the furnace. That the ignition module grounding jumper was securely fastened to the metal structure of the furnace.
What make is the furnace. Manufacture and model number? I assume the furnace is a forced air furnace.
When you get home tonight try the gas cloth dryer...
The Midwest is full of gas furnaces with electronic ignition/ignitors.... I can't recall ever reading a thread here on Agon or AA where a member experienced your same problem.
For what it is worth My furnace is a Lennox high efficiency with an electronic ignition system. It even uses a VFD to ramp down the fan speed before shutting off after a cycle.
Audio system,
Sonic frontiers Line One preamp, tubes.
ARC VT50 power amp, tubes.
The furnace does not effect my audio system whats so ever.