question about installation of 20 amp wall plug


I bought a replacement wall plug that is rated 20 amps. I installed it from a 15 amp circuit breaker, in the add it said it was ok to use in 15 or 20 amp. I pluged in a cheap intergraded amp to it and it and my speakers started popping and the amp started to smoke, I unplugged it right away. Was I wrong to assume that it would be ok coming from a 15 amp circuit, can anyone tell me what I did wrong, thanks
kedoades

Please clarify ... the PS Audio Ports are rated for both 15amp and 20amp I'm told. Can they be installed in a 15amp dedicated line?
07-09-09: Taylor514
The receptacle will accept a NEMA 5-15P or 5-20P amp plug.

Technically by code a 5-20R receptacle cannot be installed on a 120V 15 amp branch circuit.

Will it cause any kind of a fired hazard if you use one for your audio equipment? No..... If you move just remember to pull the recept and replace it with a 15 amp recept so the next guy does not see the 20 amp recept and think he has a 20 amp branch circuit available.

http://www.cryo-parts.com/ps_audio_power_port.html
.
Jim,

Is this basically what you're saying: the NEC code is written to prevent someone from unknowingly seeing the 20 Amp recepticle and believing that it is hooked up to a 20 Amp circuit?

Chuck
Chuck -- No, the main purpose of that part of the code is to prevent a high-current device, fitted with a 20 amp plug, from being plugged into a 15 amp outlet (that has 15 amp wiring). 20 amp plugs have a horizontal prong which will not allow them to be inserted into a 15 amp receptacle (which just has two parallel vertical slots, plus the safety ground contact).

Regards,
-- Al
Chuck,

Al pretty much hit the nail on the head with his answer. Though just to add to Al's response the overcurrent device, breaker, determines the branch circuit size. Even if the wire size is #12 but the breaker is a 15 amp then a 15 recept would have to be used.
Stick a volt meter inthere and measure your voltage and see if the voltage is correct. Remember, Black-Hot, White Neutral, Ground Green, Ground the bottom hole, neutral, the wide slot. Amp sounds like it had one foot in the audio casket, the other on a banana peel. A time to fry....Best of luck. Have an electrician do the work. If your home owners insurance found out you have a fire from your wiring, coverage is not likely.