Things known.
From the Cary's owners manual.
*Uses a soft start circuit. That limits inrush current.
*Has built in DC offset filter protection. (That would be after the magnetic circuit breaker)
*Uses a magnetic trip circuit breaker. (Would not be my chose)
*Cary works fine elsewhere outside OP's apartment.
*Will not work anywhere on any branch circuit in the OP's apartment without the 50' cord attached.
*Cary will not work plugged into the Synergistic Research Powercell 10se MKII power conditioner.
More questions.
What is the conductor wire gauge of the 50' extension cord?
Is the 50' cord in a coil?
Roughly the diameter size?
A 50' coil with AC current passing through it is an air core inductor..... Inductive reactance....???
Well with a magnetic trip circuit breaker Harmonics can cause them to nuisance trip.
Sailcappy, you mentioned your friend works for a power company. Does he have access to test equipment to check the power quality of the power feeding your apartment?
http://www.copperinfo.co.uk/power-quality/downloads/pqug/31-causes-and-effects.pdf
Reading from the owners manual it talks about putting the amp in "standby" mode before turning it off with the switch/circuit breaker. Not doing so leaves the amp in "Active mode" state. I assume you are powering the amp down correctly.
I ask because of the test you performed where just as the breaker tripped you notice the voltage dipped from 118V to 112V. The VD, voltage drop, was due to a spike in current. Was it the protection relay switching in the Cary amp?
Can't say 100% the VD was due to the Cary or maybe due to a high current load turning on elsewhere in your apartment. Though what are the odds it happened at the same time the breaker tripped.
.
From the Cary's owners manual.
*Uses a soft start circuit. That limits inrush current.
*Has built in DC offset filter protection. (That would be after the magnetic circuit breaker)
*Uses a magnetic trip circuit breaker. (Would not be my chose)
*Cary works fine elsewhere outside OP's apartment.
*Will not work anywhere on any branch circuit in the OP's apartment without the 50' cord attached.
*Cary will not work plugged into the Synergistic Research Powercell 10se MKII power conditioner.
More questions.
What is the conductor wire gauge of the 50' extension cord?
Is the 50' cord in a coil?
Roughly the diameter size?
A 50' coil with AC current passing through it is an air core inductor..... Inductive reactance....???
I do live in a high rise and my building said and I quote "as long as the breaker is not tripping then we do not concider you to have a problem." So much for living in a "luxury building".
Sailcappy
Well with a magnetic trip circuit breaker Harmonics can cause them to nuisance trip.
Sailcappy, you mentioned your friend works for a power company. Does he have access to test equipment to check the power quality of the power feeding your apartment?
http://www.copperinfo.co.uk/power-quality/downloads/pqug/31-causes-and-effects.pdf
Reading from the owners manual it talks about putting the amp in "standby" mode before turning it off with the switch/circuit breaker. Not doing so leaves the amp in "Active mode" state. I assume you are powering the amp down correctly.
I ask because of the test you performed where just as the breaker tripped you notice the voltage dipped from 118V to 112V. The VD, voltage drop, was due to a spike in current. Was it the protection relay switching in the Cary amp?
Can't say 100% the VD was due to the Cary or maybe due to a high current load turning on elsewhere in your apartment. Though what are the odds it happened at the same time the breaker tripped.
.