Sailcappy,
No I would not use the lightning bare 4/0 ground wire for an auxiliary equipment ground..... That could open up a whole new can of warms.
The maintained contact standby/active mode switch is in series with the rear panel breaker/switch. All amplifier loads are fed off this switch.
The soft start circuit, along with, I would imagine active sequence staging start up, keeps inrush currents controlled from the voltage readings you supplied. A 3 Volt VD on a 50' 16/3 cord is incredibly low to say the least.
Just curious is the multi meter voltage section reading true RMS?
One other test I should have mention is to check the VD with the amp playing music from a dynamic music source with the volume level set where you normally listen to music. IF the voltage were to sag below the safety limits of the amp, because of the VD of the extension cord, the amp could be damaged. If you do the test watch the meter to see if it moves around with the dynamics of the music material. Hard to believe the dynamics of the amp does not suffer because of the 50' 16/3 cord.......
Your friend does not feel safe working on the inside of a live electrical panel and that is fine.....
Better safe than sorry.....
You would need to hire an electrician to do the test for you.
Atmasphere,
The Cary 7.250 has a built in DC blocker as well as a soft start circuit.
Jim
No I would not use the lightning bare 4/0 ground wire for an auxiliary equipment ground..... That could open up a whole new can of warms.
• I attached a three way strip I had lying around into the end of the extension cord. I then plugged the Cary into one of the sockets and the voltage meter into the other.Well I would bet the switch/breaker on the back of the unit is nothing more than a main power breaker/switch disconnect.
• When turn the circuit breaker from Off to On the voltage at the end of the extension cord does not change. It remains at 118 volts. When I press the front button from Standby to Active the voltage remains at 118 volts for the 20 second duration. At that last relay click (at about 20 seconds) the voltage dropped from 118 volts down to 115 volts for split second and then back up to 118 volts.
08-22-12: Sailcappy
The maintained contact standby/active mode switch is in series with the rear panel breaker/switch. All amplifier loads are fed off this switch.
The soft start circuit, along with, I would imagine active sequence staging start up, keeps inrush currents controlled from the voltage readings you supplied. A 3 Volt VD on a 50' 16/3 cord is incredibly low to say the least.
Just curious is the multi meter voltage section reading true RMS?
One other test I should have mention is to check the VD with the amp playing music from a dynamic music source with the volume level set where you normally listen to music. IF the voltage were to sag below the safety limits of the amp, because of the VD of the extension cord, the amp could be damaged. If you do the test watch the meter to see if it moves around with the dynamics of the music material. Hard to believe the dynamics of the amp does not suffer because of the 50' 16/3 cord.......
The reason I ask is your friend qualified, confident, to perform work inside the electrical panel of your apartment? Nothing major.... Just move the hot conductor of the audio 20 amp dedicated circuit to another 20 amp breaker on the other Line, leg, bus in the electrical panel. (Providing there are any spares. If there is not a spare he could use a breaker that is being used, for the test.)
jea48
• He said all the wires are live coming in to the breaker box and it is not a good idea to switch them as there is no way to kill the current coming into the box.
Sailcappy
Your friend does not feel safe working on the inside of a live electrical panel and that is fine.....
Better safe than sorry.....
You would need to hire an electrician to do the test for you.
Atmasphere,
The Cary 7.250 has a built in DC blocker as well as a soft start circuit.
Jim